George, I will research this and let u know about 3/4 pipe. I do remember
hearing that it did not change until one of the original NBFU guys died
about 1940. Chicago pipe schedule used 3/4 pipe until about 1950.

I know the old style sprinklers went out the year I was born -- 1952.

Dave

On Thursday, April 26, 2012, George Church wrote:

> That is a relatively recent change in the good old days that I've never
> really heard definitive answers on when the 3/4" went away and when
> staggered changed.
> Before my time, I only go back to the end of 3.5" and 5", scheduled
> systems, threaded fittings and 2' away start  the grooved couplings, and
> water motor gongs.
>
> I remember thinking I was following a 669 fitter in a parking lot since
> his license plate was WMAG 300
> Water Motor Alarm Gong, 300 machine, right? What else could it be?
> Uh, Winchester magnum 300 was the rather confused answer I got.
> Oh, yeah, I guess it could be that, too.
>
> Guess its obvious I don't hunt.
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected] <javascript:;>
>
>
>
> -----Original Message-----
> From: [email protected] <javascript:;> [mailto:
> [email protected] <javascript:;>] On Behalf Of
> David deVries
> Sent: Thursday, April 26, 2012 5:04 PM
> To: [email protected] <javascript:;>
> Subject: Re: Rounding off {Squaring off?}
>
> Don't know if there is a connection without researching it, but it seems
> that staggered sprinklers went out about the same time as standard spray
> sprinklers replaced old style sprinklers and their narrower distribution
> pattern.
>
> Dave
>
> On Thursday, April 26, 2012, wrote:
>
> >
> >
> > In the "old days" heads were staggered to help even out the flow as
> > well as hasten the acttivation.
> >
> >
> >
> > David Bohannon
> >
> >
> >
> > Fire Sprinkler Plan Review City of Atlanta
> >
> >
> >
> > Department of Planning and Community Development
> >
> >
> >
> > Office of Buildings
> >
> >
> >
> > 55 Trinity Avenue
> >
> >
> >
> > Suite 3900
> >
> >
> >
> > Atlanta, GA 30303
> >
> >
> >
> > e-mail: [email protected] <javascript:;> <javascript:;>
> >
> >
> >
> > phone:  404-330-6193
> >
> >
> >
> > fax:  404-739-4172
> >
> >
> >
> >
> >
> >
> >
> > ----- Original Message -----
> >
> >
> > From: "Mark Sornsin" <[email protected] <javascript:;><javascript:;>>
> > To: [email protected] <javascript:;> <javascript:;>
> > Sent: Wednesday, April 25, 2012 4:18:18 PM
> > Subject: RE: Rounding off {Squaring off?}
> >
> > I think it ultimately goes to the fact that they needed a simple way
> > to space sprinklers and square is much easier to work with than round.
> >
> > As to the safety factor, Bruce pretty much hit it: it works. What is
> > implied is that whatever the safety factor is it must be enough. The
> > problem is, if you try to analyze the actual factor of safety you have
> > to first ignore several other potential influences on that factor.
> > Accuracy of the water supply information; actual pressure at the
> > sprinkler; choice in design area (which may be affecting the actual
> > pressure on the sprinklers); effect on calculations of including hose
> > allowances and/or domestic allowances; effect on calculations of using
> > assumed (vs actual) friction coefficients for the pipes; etc. When
> > some people make the point that sprinkler calculations have 'so much'
> > safety factor built into them they are essentially correct. But why do
> > people make those assertions? Usually it is to justify lack of
> > conformity to standards; and the problem with going down that road is
> > that none of these above influences can be precisely measured in terms
> > of additional safety factor they may or may not be providing. True,
> > some jurisdictions will waive hose allowances in calculations under
> > limited circumstances if it means saving the added cost of a pump
> > and/or tank. Certainly the knowledge of the remaining potential
> > factors of safety is a reason for doing this (on a limited basis). But
> > you don't want to push it any farther than disregarding one fairly
> measurable variable because uncertainty raises exponentially with each
> added variable.
> >
> > So the bottom line in my view is that one could certainly do a
> > mathematical exercise where they calculate the safety factor of all of
> > the overlap in sprinkler sprays; but first they would have to make
> > assumptions about those other influences. By the time they are done
> > doing that, the exercise is nearly worthless, except as a bit of
> > intrigue for those of us in the business.
> >
> > BTW - you can go to some manufacturer's web sites and view sprinkler
> > spray patters. If you look at the Viking M 1/2 in. upright, you'll see
> > that at 7psi, the spray from about 8 ft. above the floor reaches just
> over 9 ft.
> > from the centerline of the sprinkler. In a Light Hazard Occupancy,
> > that overlaps the 7'-6" maximum distance, but does not reach the
> > maximum diagonal distance of 10.6 ft.  At 30 psi, you get closer to the
> 10.6 ft.
> > Obviously, at smaller spacing, the overlap increases (another variable
> > to consider).
> >
> > Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.|
> > Fargo, ND [email protected]
> >
> >
> > -----Original Message-----
> > From: [email protected] <javascript:;> [mailto:
> > [email protected] <javascript:;>] On Behalf Of
> Bruce Verhei
> > Sent: Tuesday, April 24, 2012 12:51 PM
> > To: [email protected] <javascript:;>
> > Subject: Re: Rounding off {Squaring off?}
> >
> > I've read in the past that this fell in the not well understood effect
> > category when engineers have desired to model how sprinklers actually
> work.
> > This seems to be difficult.  They say something that ends with but
> > sprinklers installed and maintained to standards have a remarkable
> > record of controlling fires in buildings.
> >
> > I want to buy one of the square heads.  Are the threads square too?
> >
> > Bruce
> >
> > Sent from my Motorola ATRIXT 4G on AT&T
> >
> > -----Original message-----
> > From: Thomas Watt <[email protected] <javascript:;>>
> > To: [email protected] <javascript:;>
> > Sent: Tue, Apr 24, 2012 13:05:01 GMT+00:00
> > Subject: Rounding off {Squaring off?}
> >
> > I had a brain-fart and came up with this question for the forum.
> > Especially the engineers.  Since sprinklers, in general, throw in a
> > circular pattern, and we calc the sprinklers as squares, there is
> > always overlap so we are by default miscalculating a percentage of the
> density.
> > Has anyone ever calculated the safety factor effect by ignoring the
> > arcs outside the square???
> >
> > Thomas
> > A+ fitter/Foreman
> > No work in Orlando, FL area
> > Willing to relocate
> > -------------- next part -------------- An HTML attachment was
> > scrubbed...
> > URL: <
> > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> > hments/20120424/5639c5b1/attachment.html
> > >
> > ________________________URL: <
> > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> > hments/20120426/f2dde620/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected] <javascript:;> <javascript:;>
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120426/c9ca1cc2/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] <javascript:;>
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] <javascript:;>
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120426/787dd92e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to