C.,
I may be off but check the electrical code, NFPA70.
They discuss clearances around and above distribution panels.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Ford, Charles
> Sent: Friday, May 04, 2012 7:51 AM
> To: [email protected]
> Subject: RE: High voltage clearances
>
> I thought NFPA 13 had a chart specifying clearance distance from
> sprinkler piping and hi voltage open bus bars. I can't find it. There
> is one in 12 ( co2 systems) but not eaxctly the same thing. I have a
> partner asking if there is a minimum distance. any thoughts out there?
>
> C. Burton Ford
> Nicet Certified
> Special Hazards IV
> Fire alarm IV
> Sprinkler III
> Water Based Inspections I
> NFPA Certified Fire Protection Specialist [CFPS] Cintas Fire Protection
> 1038 Conshohocken Road
> Conshohocken ,PA 19428
> 610-233-1400
> Fax 610-233-1401
> ________________________________________
> From: [email protected] [sprinklerforum-
> [email protected]] On Behalf Of Stewart Kidd [stewart-
> [email protected]]
> Sent: Monday, April 30, 2012 6:26 PM
> To: [email protected]
> Subject: Re: Aerosol vs Halocarbon/Inert extinguishing agents - Firepro
> Answers - Please comment!
>
> Reza
>
> 1. Why does IBM use sprinklers (with water) in all its factories and
> units ?
> 2.Data can be recovered from hard drives which have been wetted by
> sprinklers or fire hoses - this is not true of powders 3. Clean up of
> powder even when there has been no fire is very expensive as the powder
> is hygroscopic.
> 4. Tests in Norway and by US GSA suggest that powder is damaging for
> heritage objects - especially paintings, glass and china
>
> Best
>
> Stewart
> On 30 Apr 2012, at 20:34, Ed Vining wrote:
>
> > 1. Being OK for electrical doesn't automatically make it OK for
> > electronics or systems with moving parts.
> >
> > 3. Continued training and awareness can't be counted on. George
> > Church's anecdote about the fire alarm in a restaurant proves that
> > people are dumber than sheep. Sheep will at least follow the leader.
> >
> > 4. There isn't always a huge mess. Just because aerosol might not
> be
> > worse than some of its competitor doesn't make the method of choice.
> >
> > Ed Vining
> > 4819 John Muir Rd
> > Martinez CA 94553
> > 925-228-8792
> > Cell 925-787-0465
> >
> >
> > On Mon, Apr 30, 2012 at 12:17 PM, Reza Esmaeili
> > <[email protected]>wrote:
> >
> >>
> >>
> >>
> >>
> >>
> >> I have contacted Firepro which is making UL listed Aerosol units and
> >> asked them the below questions, I would appreciate your comments on
> their answers:
> >>
> >> 1- According to NFPA 2010 "Aerosol fire-extinguishing agents shall
> >> not be used on fires involving Deep-seated fires in Class A
> >> materials", then do you offer Firepro units to be used in Paper/Book
> >> Archive Rooms facing deep seated fire in class A material?
> >> ANSWER: All fixed gas extinguishing systems, as well as aerosol
> >> systems are tested and certified for Class A, surface burning fires.
> >> The test protocols for polymeric materials and wood specify
> >> pre-burning times from
> >> 3.5 min. to 6 min. respectively. Longer burning time is considered
> as
> >> deep seated fires.
> >>
> >> 2- According to NFPA 2010 "The potential adverse effects of agent
> >> particulate residue on sensitive equipment shall be considered",
> then
> >> do you offer Firepro units to be used in Server Rooms with sensitive
> >> hard disks.
> >> ANSWER: FirePro has been independently tested by NLR (Dutch National
> >> Aerospace Laboratory) and TNO (Netherlands Organisation for Applied
> >> Scientific Research), proving that there are no effects on (a)
> >> corrosion of sensitive electrical components, and (b) the operation
> >> of electrical equipment, respectively.
> >>
> >> 3- According to NFPA 2010 "aerosol systems shall be used in normally
> >> unoccupied areas because of visibility obscuration and the potential
> >> health effects of accidental exposure to the agent" then do you
> >> offer Firepro units to be used in Monitoring Rooms where people
> usually exist?
> >> ANSWER: Please see detailed response
> >> www.esmaeili.ir/Aerosol-in-occupied-areas.pdf
> >>
> >> 4- Do you offer Firepro units to be in a place where dust or residue
> >> is a matter of concern and clean-up procedure costs too much like a
> >> museum, art gallery?
> >> ANSWER: Please note, after a fire, there is a huge mess, Therefore,
> >> after a fire, you are going to clean anyway ! FirePro has been used
> >> in museums and old cultural buildings, etc, the consequences of
> >> other extinguishing agents such as halocarbons, especially in
> >> electrical/electronic applications, can be more serious; of
> paramount
> >> importance is the liberation/formation of HF (hydrogen fluoride) and
> CO at high temperatures.
> >> So it is best to sweep/dust the FP particles than to damage/destroy
> >> the electrical components with the decomposition of halocarbons/FM-
> 200.
> >>
> >>
> >> Best,
> >> Reza
> >> -------------- next part -------------- An HTML attachment was
> >> scrubbed...
> >> URL: <
> >>
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> >> chments/20120430/aca9680e/attachment.html
> >>>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> > -------------- next part -------------- An HTML attachment was
> > scrubbed...
> > URL:
> >
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> > chments/20120430/55489afc/attachment.html>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> This e-mail transmission contains information that is intended to be
> confidential and privileged. If you receive this e-mail and you are
> not a named addressee you are hereby notified that you are not
> authorized to read, print, retain, copy or disseminate this
> communication without the consent of the sender and that doing so is
> prohibited and may be unlawful. Please reply to the message
> immediately by informing the sender that the message was misdirected.
> After replying, please delete and otherwise erase it and any
> attachments from your computer system. Your assistance in correcting
> this error is appreciated.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum