That is high to anyone who comes in direct contact with that voltage so it
is good to be careful.  But the question remains, is it open (unprotected)
or enclosed.  All the bus bars I have seen are enclosed.  You can crawl
over them, touch them, since the enclosure is designed to keep people away
from the uninsulated bars inside.  Once you remove the covers, such as to
install a bus tap switch, you have to de-energize the bus bar.

 Still not sure of the question.  Is the issue can you install sprinkler
piping close to these bus bars without the fitter being in danger?  That
would be a site-specific safety question.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]



From:   "Ford, Charles" <[email protected]>
To:     "[email protected]"
            <[email protected]>
Date:   05/04/2012 02:07 PM
Subject:        RE: High voltage clearances
Sent by:        [email protected]



The only voltage mentioned was 440 Vac. Thet's high to sprrinkler techs and
fire alarm techs.


C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________
From: [email protected]
[[email protected]] On Behalf Of [email protected]
[[email protected]]
Sent: Friday, May 04, 2012 11:07 AM
To: [email protected]
Subject: RE: High voltage clearances

Please clarify what you mean by high-voltage.  NEC says over 600 V is high
voltage, but the typical bus bar in industry is only 480 volts.  Not high
voltage.  And they are usually not open to the world.  Usually some kind of
enclosure.  If open, then that could be a bigger hazard to personnel.

If really high voltage and uninsulated then several feet of clearance would
be needed.  We have all seen the videos of the guy in his back yard and the
ladder that comes close to the overhead line.  The arc starts forming well
before the ladder contacts the line.  Is that what you are referring to?

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]



From:   "Ford, Charles" <[email protected]>
To:     "[email protected]"
            <[email protected]>
Date:   05/04/2012 06:55 AM
Subject:        RE: High voltage clearances
Sent by:        [email protected]



I thought NFPA 13 had a chart specifying clearance distance from sprinkler
piping and hi voltage open bus bars. I can't find it. There is one in 12
( co2 systems) but not eaxctly the same thing. I have a partner asking if
there is a minimum distance. any thoughts out there?

C. Burton Ford
Nicet Certified
Special Hazards IV
Fire alarm IV
Sprinkler III
Water Based Inspections I
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401
________________________________________
From: [email protected]
[[email protected]] On Behalf Of Stewart Kidd
[[email protected]]
Sent: Monday, April 30, 2012 6:26 PM
To: [email protected]
Subject: Re: Aerosol vs Halocarbon/Inert extinguishing agents - Firepro
Answers - Please comment!

Reza

1. Why does IBM use sprinklers (with water) in all its factories and
units ?
2.Data can be recovered from hard drives which have been wetted by
sprinklers or fire hoses - this is not true of powders
3. Clean up of powder even when there has been no fire is very expensive as
the powder is hygroscopic.
4. Tests in Norway and by US GSA suggest that powder is damaging for
heritage objects - especially paintings, glass and china

Best

Stewart
On 30 Apr 2012, at 20:34, Ed Vining wrote:

> 1.  Being OK for electrical doesn't automatically make it OK for
> electronics or systems with moving parts.
>
> 3.  Continued training and awareness can't be counted on.  George
Church's
> anecdote about the fire alarm in a restaurant proves that people are
dumber
> than sheep.  Sheep will at least follow the leader.
>
> 4.  There isn't always a huge mess.  Just because aerosol might not be
> worse than some of its competitor doesn't make the method of choice.
>
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> Cell 925-787-0465
>
>
> On Mon, Apr 30, 2012 at 12:17 PM, Reza Esmaeili
> <[email protected]>wrote:
>
>>
>>
>>
>>
>>
>> I have contacted Firepro which is making UL listed Aerosol units and
asked
>> them the below questions, I would appreciate your comments on their
answers:
>>
>> 1- According to NFPA 2010 "Aerosol fire-extinguishing agents shall not
be
>> used on fires involving Deep-seated fires in Class A materials", then do
>> you offer Firepro units to be used in Paper/Book Archive Rooms facing
deep
>> seated fire in class A material?
>> ANSWER: All fixed gas extinguishing systems, as well as aerosol systems
>> are tested and certified for Class A, surface burning fires. The test
>> protocols for polymeric materials and wood specify pre-burning times
from
>> 3.5 min. to 6 min. respectively. Longer burning time is considered as
deep
>> seated fires.
>>
>> 2- According to NFPA 2010 "The potential adverse effects of agent
>> particulate residue on sensitive equipment shall be considered", then do
>> you offer Firepro units to be used in Server Rooms with sensitive hard
>> disks.
>> ANSWER: FirePro has been independently tested by NLR (Dutch National
>> Aerospace Laboratory) and TNO (Netherlands Organisation for Applied
>> Scientific Research), proving that there are no effects on (a) corrosion
of
>> sensitive electrical components, and (b) the operation of electrical
>> equipment, respectively.
>>
>> 3- According to NFPA 2010 "aerosol systems shall be used in normally
>> unoccupied areas because of visibility obscuration and the potential
health
>> effects of accidental exposure to the agent"  then do you offer Firepro
>> units to be used in Monitoring Rooms where people usually exist?
>> ANSWER: Please see detailed response
>> www.esmaeili.ir/Aerosol-in-occupied-areas.pdf
>>
>> 4- Do you offer Firepro units to be in a place where dust or residue is
a
>> matter of concern and clean-up procedure costs too much like a museum,
art
>> gallery?
>> ANSWER:  Please note, after a fire, there is a huge mess, Therefore,
after
>> a fire, you are going to clean anyway ! FirePro has been used in museums
>> and old cultural buildings, etc,  the consequences of other
extinguishing
>> agents such as halocarbons, especially in electrical/electronic
>> applications, can be more serious; of paramount importance is the
>> liberation/formation of HF (hydrogen fluoride) and CO at high
temperatures.
>> So it is best to sweep/dust the FP particles than to damage/destroy the
>> electrical components with the decomposition of halocarbons/FM-200.
>>
>>
>> Best,
>> Reza
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: <
>>
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120430/aca9680e/attachment.html


>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120430/55489afc/attachment.html

>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not a
named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be unlawful.
Please reply to the message immediately by informing the sender that the
message was misdirected.  After replying, please delete and otherwise erase
it and any attachments from your computer system.  Your assistance in
correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not a
named addressee you are hereby notified that you are not authorized to
read, print, retain, copy or disseminate this communication without the
consent of the sender and that doing so is prohibited and may be unlawful.
Please reply to the message immediately by informing the sender that the
message was misdirected.  After replying, please delete and otherwise erase
it and any attachments from your computer system.  Your assistance in
correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to