While mostly academic in this exercise, NFPA 13 2010 6.2.7.1 requires
them to be metal, or listed even for non recessed escutcheons.  Assuming
you use genuine 401s it's fine, but there are some plastic knockoffs
last I looked and they aren't listed as far as I'm aware. 


-Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc
[email protected]
Desk: 317-651-0596
Cell: 317-439-2695

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eric
Tysinger
Sent: Tuesday, July 31, 2012 8:59 AM
To: [email protected]
Subject: RE: EC Heads with 401 style plates?

Only recessed plates have to be listed with the particular sprinkler. If
the sprinkler is installed up to the max deflector distance
(non-recessed) then the plates are only cosmetic at that point. If I am
not mistaken the flat plates and 401's are not even required to be
listed. This is stated in 13, I just don't have my book around to look
up the section.

Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire
Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Tuesday, July 31, 2012 8:17 AM
To: [email protected]
Subject: EC Heads with 401 style plates?

NFPA #13 says that the maximum deflector distance for EC heads
(non-comb, unobstructed const) is 12". All of the EC Pensents I am
looking at only have Flat Esc. or Semi-rec plates listed.

Can you use 401 style plates with these heads even thought they are not
specifically listed? My thoughts are that you can because if you used
bare pipe you place the head 12" below the ceiling, so if that is true
and you choose to cover the pipe with Deep Plates, it should not be a
problem.

Thanks,

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160
McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120731/27a6be42/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to