NFPA 13, 2007.
Please look at 6.2.7, in a nut shell.
If not recessed, flush or concealed the only listing requirement is for 
non-metallic escutcheons.


Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Morey, Mike
Sent: Tuesday, July 31, 2012 2:22 PM
To: [email protected]
Subject: RE: EC Heads with 401 style plates?

While mostly academic in this exercise, NFPA 13 2010 6.2.7.1 requires them to 
be metal, or listed even for non recessed escutcheons.  Assuming you use 
genuine 401s it's fine, but there are some plastic knockoffs last I looked and 
they aren't listed as far as I'm aware. 


-Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc
[email protected]
Desk: 317-651-0596
Cell: 317-439-2695

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Eric Tysinger
Sent: Tuesday, July 31, 2012 8:59 AM
To: [email protected]
Subject: RE: EC Heads with 401 style plates?

Only recessed plates have to be listed with the particular sprinkler. If the 
sprinkler is installed up to the max deflector distance
(non-recessed) then the plates are only cosmetic at that point. If I am not 
mistaken the flat plates and 401's are not even required to be listed. This is 
stated in 13, I just don't have my book around to look up the section.

Eric Tysinger CET
NICET III - 108988
Designer/Project Manager - Fort Myers Branch Wayne Automatic Fire Sprinklers, 
Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, July 31, 2012 8:17 AM
To: [email protected]
Subject: EC Heads with 401 style plates?

NFPA #13 says that the maximum deflector distance for EC heads (non-comb, 
unobstructed const) is 12". All of the EC Pensents I am looking at only have 
Flat Esc. or Semi-rec plates listed.

Can you use 401 style plates with these heads even thought they are not 
specifically listed? My thoughts are that you can because if you used bare pipe 
you place the head 12" below the ceiling, so if that is true and you choose to 
cover the pipe with Deep Plates, it should not be a problem.

Thanks,

--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie 
Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120731/27a6be42/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to