In 1973 there were three ordinary, OH1, 2 & 3, and three extra, EH1, 2 & 3, hazard groups. They were all (respectively) scheduled the same. Area of coverage has no relevance to the schedule itself other than there is a maximum for each group (LH (225 sqft), OH (130sqft), & EH (100 sqft)). There is a schedule for each group for steel and for copper, and a modified schedule for heads covering the floor only, or heads covering the floor and an interstitial space.
On Fri, Aug 31, 2012 at 11:40 AM, Richard Carr <[email protected]> wrote: > You may not be able to tell if is group 1 or 2 because the schedule was > the same, the 100 sq ft spacing indicates it was high piled storage. > > Richard Carr, SET > Branch Manager > Cox Fire Protection, Inc > 6555 Grace Lane. > Jacksonville, Fl. 32205 > [email protected] > 904-781-8227 > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Thomas > Reinhardt > Sent: Friday, August 31, 2012 2:31 PM > To: [email protected] > Subject: Pipe Schedule Question > > I'm reviewing old pipe schedule plans from 1973.The sprinkler plans say" > System classification 100 sqft. Per sprinkler with O.H. pipe sizing." My > question is the plans do not mention Group 1 or Group 2.How do I know if > the O.H.(ordinary hazard is group 1 or 2)? Based on NFPA 13(2010) > different occupancies are allowed for group 1 and group 2.Thanks > Wheeling Fire Inspector Tom Reinhardt > 2 Community Boulevard > Wheeling, IL 60090 > 847-499-9067 > > > ________________________________ > IMPORTANT NOTICE: This e-mail message is intended to be received only by > persons entitled to receive the confidential information it may contain. > E-mail messages may contain information that is confidential and legally > privileged. Please do not read, copy, forward, or store this message > unless you are an intended recipient of it. If you have received this > message in error, please forward it to the sender and delete it > completely from your computer system. > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach > ments/20120831/70c052b2/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120831/12d23506/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum