Dear Sirs:

As always, It is an honor writing to this forum. A customer has a
Cyclopentane inside storage, 110 square meters of area, solid pile on wood
pallet, 4 highs, to complete 15 feet of top of storage, with 26 feet
maximum ceiling high. Cyclopentane is in metallic relieving 55 gallons
drums, 4 drums per pallets, 16 drums for storage load at 4 higs as I said
before. Cyclopentane is a flammable class IB liquid according to NFPA 30.
According to the mentioned standard, storage must have a 0.60 over 3000
water-foam sprinkler protection, but the pump (you can find the pump and
current fire protection system in this link
http://www.mediafire.com/?jcpmvttv8v634 )  that is NOT a UL or/and FM one,
doesn’t achieve the flow and pressure requirements, even it can be capable
to supply the pressure for a traditional foam system (in line proportioner)
. I tried with both traditional foam system and high expansion foam but
system’s pressures (at least in my hyd calculations)  don’t fit the
requirements. However, I saw a Ansul AROUND-THE-PUMP foam system that could
be a solution, but the data sheet doesn’t say anything about industrial
application, it only show fire truck applications. So, I have two question
for the forum: 1.- May I use AROUND-THE-PUMP foam systems for a industrial
applicattions, considering that the pump is about 100 meters away from the
storage? (the fire system drawing is in the above link
http://www.mediafire.com/?jcpmvttv8v634 ) 2.- Can you make recommendations
for this storage’s fire protection system without changing the pump? (the
customer doesn’t have enough money to buy another one, he only wants the
storage protection without  expending in any other system). Thanks in
advance and happy Sunday…


-- 
----------

Saludos,

PD. Agradecemos que incluya en su respuesta a este correo la dirección
[email protected] . Disculpe las molestias.


*Ing. José Prada*
*Consultor Sistemas Contra Incendios - Especialista en SHA*
Miembro NFPA 2468443 - RNC Sencamer N° 344
OSHA CERTIFIED 900144392 – INPSASEL ARA079660090
Teléfonos Venezuela: +58.244.661.80.61 - +58.416.432.63.10 -
+58.412.146.58.05
Telefonos Colombia:  (+57) 320.272.85.29 - (+57) 300.624.03.06 - (+57)
311.541.10.03
MSN Messenger: [email protected]
Skype: jose.prada

BB PIN: 297AFC2B
Instale http://www.whatsapp.com/ en su celular y agregueme a su libreta con
el +57.311.541.10.03  o el +57.300.624.03.06
Twitter: josegpradar

VISITENOS EN www.joseprada.com
____________________________________________

Estamos trabajando constantemente para proveer la mayor cantidad de
satisfacción a nuestros clientes.
___________________________________

Nota: Si ha recibido un archivo anexo con extensión .pdf y no posee el
Acrobat Reader, descarguelo en
http://www.adobe.es/products/acrobat/readstep2.html
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120902/d6842990/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to