Since it’s the first time I’m doing this I would like to double check with
the forum if I have it right………

 

I have a storage area to protect that’s over 16’ deep and 22’ high, 2
shelves and a 5’ aisle. The commodity is a non-encapsulated/class IV, we
utilized table 16.2.1.3.3.2 figure 16.2.1.3.2 (d) Curve C  which is a .39
over 2000² and section 16.2.1.3.4.6 to reduce density with 40% for in-rack
sprinklers which totals to .234 over 2000² is there a special requirement
other than the 18” for clearance from ceiling sprinkler to storage?

 

for in-rack sprinklers [16.2.4.3] I know that I need to calculate 14
sprinklers (seven on top two levels (which in my case we only have 2 levels
of shelving) and I know that I need 15 psi  according to section 16.2.4.4
what I don’t get is what’s the GPM or density requirements?

 