It is allowed if done per NFPA 13 (2010) Section 9.1.1.2 as indicated in Annex 
A.9.1.1.7.   Additionally, pilot line piping can be supported from the system 
it serves per Section 8.14.10 and NFPA 15 (2010) Section 6.5.1.5.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Monday, September 10, 2012 3:18 PM
To: [email protected]
Subject: Hangin' OUT?

Just curious here....

Has anyone ever hung pipe from pipe?  Not trapeze, but a situation under 1" and 
1ΒΌ" branchlines doubling back to catch new head locations....




Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 
44136       440 238-4800     Fax 440 238-4876
____________________________________________________________________