UFC 3-600-01 overrides all others. See Para 1-3 for a hierarchy of applicable codes and standards. It refers to NFPA(latest editions) except as modified. It also refers to ETL 02-15 -Engineering Technical Letter regarding Fire Protection Engineering Criteria - New Aircraft Facilities. IFC applicability is discussed as pertaining to the IBC which is specifically referenced in UFC 3-600-01. You should have additional guidance provided to you by an EOR. Is there none? I would not pursue such a project without it.
Ryan Hinson Burns & McDonnell Direct: 952-656-3662 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jay White Sent: Tuesday, September 25, 2012 2:24 PM To: [email protected] Subject: Blast Booth Air Force Baser hanger Blast Booth. Would the requirements for fire protection fall under NFPA, UFC, or IFC code? Or all three? Which one addresses the design requirements? Jay White Dynamic Fire Protection 9771 Highway 25 South Starkville, MS 39759 PH: 662-312-2426 FAX: 662-324-1545 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120925/0eb0e8a5/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum