First, why would you add air when the N2 alone is the cat's meow to minimize 
corrosion?
Next, with an AMD it's an auto air supply until its empty. If they keep a spare 
bottle and there's a low air whistle, and you haven't installed a leaker, then 
they can change it when they come in for work the next day. That is like a 
dream dry sys air supply, you could even connect the reserve so if the one guy 
who knows how to do it is on vacation, they don't freeze the system. Someone 
could keep an eye on it, too- like if they have quarterlies...
So you can tailor a setup that makes sense and is reliable and adds longevity. 
You can't account for every situation so I'm not going to try to address the 
code side.

We used bottles to avoid an air compressor in explosion-proof rated areas. Back 
when the WMAG was the only alarm days.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis
Sent: Thursday, October 04, 2012 4:46 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Air Supply

Guess I am confused now. 5.1 is Labeled "Automatic". Do sections 7.2.6.2.1 &
2 apply? (07)
7.2.6.7 "Nitrogen" references you back to 5.1 "Automatic..."

R/
Matt

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Thursday, October 04, 2012 3:54 PM
To: sprinklerforum@firesprinkler.org
Subject: Air Supply

Looking over a job where the EOR wants to use cylinders to supply the air for a 
dry system.  There is plenty of power to the building so that's not the issue.  
They are showing lab air cylinders from both air (NC) and nitrogen (NO) into an 
AMD into the system.  I get automatic air is not required.  But I'm seeing NFPA 
13 '12-7.2.6.5.1 limiting air supply when AUTOMATIC to dependable shop system 
or a compressor.  I don't see bottles being allowed.  Or that is to say I don't 
see bottles as being a dependable shop system.

I assume some of you have done bottles for the air to a dry system?  As I read 
you can have them if someone manually opens a valve and refills the system when 
needed?  Of course this is even confusing.  Is there something on a manual fill 
system that requires daily checking?  Or are they relying on the low pressure 
alarm to note when time to refill?  Actually, the low pressure alarm isn't even 
required, right, so are they waiting for a system trip to know when to add air?

If manual is allowed isn't an AMD off a bottle a little better but not quite 
the full blown compressor?  Why would they restrict the middle on the order of 
worst to best?

Who wants to straighten me out 'cuz none of us here have ever seen bottles used 
on a system?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com<mailto:ccah...@burnsmcd.com>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN




-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121004/0e12d424/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to