I'd say they want the Fire Sprinklers to SHUT-OFF if the City water drops
below 20 psi.

They must consider back-siphonage into the CIty Water system more dangerous
than
the fire that is NOT getting water poured on it from Sprinklers.

I wonder if the Fire Dept. has the same instructions?

Jeff Garrison
Detroit


On Mon, Nov 12, 2012 at 12:19 PM, Timothy W Goins <[email protected]> wrote:

> How are others addressing the 20 PSI minimum operating pressures of the
> fire
> sprinkler system? Here is a quote from a spec that I have received.
>
> "The fire protection systems shall not be designed to operate if the
> residual
>
> pressure of the existing water service falls to 20 psi or lower at design
> flow
>
> requirements."
>
>
>
> Timothy W Goins
> A & T Services
>
>
>
> "For I am not ashamed of the gospel of Christ: for it is the power of God
> unto salvation to everyone that believeth;." KJV Romans 1:16
>
>
>
> Reply to   <mailto:[email protected]> mailto:[email protected]
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/9c2eef0f/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/2378f6b7/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to