At  an occupied structure fire in phoenix they will pump the from the main 
until the chunks of debris stall the impeller.
Mark at Aero

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 12, 2012 12:14 PM
To: [email protected]
Subject: RE: 20 PSI Minimum

If the water department mandate is to not allow the municipal supply to drop 
below 20 psi the FD has no choice but to comply and bring in tankers if 
necessary.  This was the plan for a project we had about three years ago where 
this very requirement was in place.  The FD knew of the water purveyor's 20 psi 
requirement and had a contingency plan for areas of the municipality where the 
water supply was weak.  This is typically not a surprise to the FD and the 
water dept.  The surprise comes to those of us on the outside who aren't 
familiar with the local rules and regulations.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 12, 2012 12:56 PM
To: [email protected]
Subject: RE: 20 PSI Minimum

So in this situation, should the responding fire company stop boosting the FDC 
from a hydrant at 19 PSI? None that I know would stop.
Mark at Aero

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, November 12, 2012 10:51 AM
To: [email protected]
Subject: RE: 20 PSI Minimum

Are we talking a low suction cut-off, but of the supply NOT suction to a pump?
I suppose the water co wouldn't want the pressure to go below 20, but it flies 
in the face of all we stand for to have a shut-off inserted for stopping the 
operation of the sprinkler system if the supply pressure is below 20 PSI. You 
could save a lot of first floor lives with 20 PSI.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Owen Evans
Sent: Monday, November 12, 2012 12:34 PM
To: [email protected]
Subject: Re: 20 PSI Minimum



Hello Timothy,
This is the first post I've seen on 20 psi minimum. Can you give me more 
details on this?
Thanks,
Owen Evans





-----Original Message-----
From: Timothy W Goins <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Nov 12, 2012 9:23 am
Subject: 20 PSI Minimum


How are others addressing the 20 PSI minimum operating pressures of the fire 
sprinkler system? Here is a quote from a spec that I have received.

"The fire protection systems shall not be designed to operate if the residual

pressure of the existing water service falls to 20 psi or lower at design flow

requirements."

 

Timothy W Goins
A & T Services

 

"For I am not ashamed of the gospel of Christ: for it is the power of God unto 
salvation to everyone that believeth;." KJV Romans 1:16

 

Reply to   <mailto:[email protected]> mailto:[email protected]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/9c2eef0f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121112/3adace85/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to