This one came across for bidding and the specs / design are from the
consultant's drawings.  The overall building height requires the use of
K25 ESFR sprinklers.  The consultant has specified that K25 ESFR
sprinklers are to be used only in the high bay of the building at
pressure "A" and K17 ESFR sprinklers at pressure "B" are to be used for
the lower areas.  The building is open joists / girders type of
construction.  Can this even be done?  If so, I imagine that 3 calcs
would be in order.  A K25 calc, K17 calc, and the area where they would
overlap (ie 15ft beyond).

Anyone else come across something like this?

Thanks,

 