Yes, we have come across it many times. Some buildings have ridge heights over 
40' and eave heights under 40'. There is no good way, that we have found, to 
mix k17's and k25's in the same system. The higher pressure required by the 
k17's causes the K25's to over flow. We always change at system breaks to k17's 
once the roof height is less than 40'. I don't see the need to be concerned 
about going 15 ft beyond.

Ron Fletcher
Aero Phoenix 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Thursday, January 31, 2013 10:08 AM
To: SprinklerFORUM
Subject: Mixing ESFR sprinklers due to building height

This one came across for bidding and the specs / design are from the 
consultant's drawings.  The overall building height requires the use of
K25 ESFR sprinklers.  The consultant has specified that K25 ESFR sprinklers are 
to be used only in the high bay of the building at pressure "A" and K17 ESFR 
sprinklers at pressure "B" are to be used for the lower areas.  The building is 
open joists / girders type of construction.  Can this even be done?  If so, I 
imagine that 3 calcs would be in order.  A K25 calc, K17 calc, and the area 
where they would overlap (ie 15ft beyond).

Anyone else come across something like this?

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130131/7b637fe5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to