Rod, section 6.6.1 (13R 2010) may be what you're looking for.

Ed Kramer

> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Rod DiBona
> Sent: Wednesday, February 13, 2013 9:34 AM
> To: [email protected]
> Cc: Brent Zimiga
> Subject: RE: Exterior closets....again but different
> 
> Steve,
> 
> Thank you for your response. I do agree that the contested closets are
> outside the dwelling unit. I am looking but haven't found where 13R says
> that areas outside the dwelling unit shall be PROTECTED by 13. I see
> 6.8.2.1 that says "For areas outside the dwelling unit, the design
> discharge and design area criteria shall comply with NFPA 13"....No
> mention of coverage?... For example, we don't sprinkler concealed
> combustible and attics in 13R which are outside the dwelling unit. So
> this is the heart of the issue does chapter 8 of 13 apply? Is so where
> does 13R state that it does apply for protection of areas? If it does
> apply, then the 13R exemptions for other areas outside the dwelling unit
> trump 13 requirements? Not trying to be difficult and this is not a big
> add to the project but truly want to come to an understanding on this
> one. Wonder why the closets on the decks would be exempted but not a
> breezeway? Egress? Thanks!
> 
> Rod at Rapid
> 
> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-
> [email protected]] On Behalf Of Steve Leyton
> Sent: Tuesday, February 12, 2013 10:52 PM
> To: [email protected]
> Subject: RE: Exterior closets....again but different
> 
> I agree with the AHJ.   Exception to closets on exterior balconies
> presumes they are within (or directly communicating with) dwelling unit.
> If you agree that the contested closets are outside of the dwelling
> unit, where is the exception in 13 that would not require sprinklers in
> these compartments?  Methinks you're trying to split hairs with the
> "design criteria" intent argument - what do you mean by that, exactly?
> If hydraulics, then the answer is yes, but 13R also states that areas
> outside the dwelling unit shall be protected per 13, so I think that
> Chapter 8 of 13 applies, period.
> 
> The foregoing is my opinion only, and does not necessarily represent the
> opinion or intent of the Technical Committee on Residential Sprinkler
> Systems.
> 
> Steve L.
> 
> 
> -----Original Message-----
> From: [email protected] on behalf of Rod DiBona
> Sent: Tue 2/12/2013 4:25 PM
> To: [email protected]
> Subject: Exterior closets....again but different
> 
> NFPA 13R 2007- New apartment building with a breezeway on the bottom
> level that is enclosed and protected with dry sidewalls. 2 closets (one
> plumbing and the other electrical data) in that breezeway that only open
> to the breezeway. No fuel fired equipment. No heating or air
> conditioning equipment. Had it in my mind that these closets would not
> have to be sprinklered. Fire marshal is disagreeing. After review I am
> not so sure. Seems like the intent is to not require protection but by
> the letter I can't quite get there. Am I missing something?
> 
> 2007 NFPA 13R 6.9.6 - "Sprinklers shall not be required
> in............(last sentence) ... "and other concealed spaces that are
> not intended for living purposes or storage and do not contain fuel
> fired equipment." -   He pointed out that a closet is not a concealed
> space...... Ok then.....
> 
> 2007 NFPA 13R 6.9.7 " Sprinklers shall not be required in closets on
> exterior balconies, regardless of size, as long as there are no doors or
> unprotected penetrations from the closet directly into the dwelling
> unit. - His point is that these closets are not on exterior
> balconies....
> 
> He says that it is outside the dwelling unit and therefore protected by
> NFPA 13. My comment is that I believe 2007 NFPA 13R only requires the
> "design criteria" of 13 to be followed for areas outside the dwelling
> unit.  Clarified in section A.6.8.2.
> 
> He says show me in 13R where you can exclude.....
> 
> 
> Thoughts?
> 
> 
> [Description: LOGO_10]
> Rod DiBona
> Vice President
> Rapid Fire Protection
> office : (605)348-2342
> fax : (605)348-0108
> cell : (605)391-3553
> www.rapidfireinc.com<http://www.rapidfireinc.com>
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20130213/ae9e854f/attachment.html>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 6561 bytes
> Desc: image001.jpg
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20130213/ae9e854f/attachment.jpg>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: winmail.dat
> Type: application/ms-tnef
> Size: 4240 bytes
> Desc: not available
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20130212/786c66f1/attachment.bin>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to