Ah, Bruce has the real question. Does Ken have the answer but is playing
Johnny Tightlips?

On Thu, Mar 14, 2013 at 4:22 PM, Bruce Verhei <[email protected]> wrote:

> What problem is this section trying to solve?
> Bv
>
> -----Original message-----
> From: "Cahill, Christopher" <[email protected]>
> To: "[email protected]" <[email protected]>,
> "[email protected]" <[email protected]>
> Sent: Thu, Mar 14, 2013 15:28:26 GMT+00:00
> Subject: RE: Phantom Flow
>
> I'd argue you are OK because you are not using density/area method.
> Section always talks about area.  You have no minimum area.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Thursday, March 14, 2013 9:58 AM
> To: [email protected]; [email protected]
> Subject: RE: Phantom Flow
>
> Wow. We are doing a project with a canopy that I don't think needs to be
> sprinkler but that isn't the point. The canopy is 3'-11" wide, sloped
> greater than 2 in 12, requires a dry system and is 600' long. Section
> 11.2.3.4.2 requires 7 heads maximum. Would 23.4.4.1.1.4 apply and if so how
> would it be applied? The minimum design area would be 0.20 gpm over 2,535
> sqft. The canopy is 2,400 sqft and only has one branch line with 48
> sprinklers.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ed Kramer
> Sent: Wednesday, March 13, 2013 6:51 PM
> To: [email protected]
> Subject: RE: Phantom Flow
>
> Chris, the way I read 23.4.4.1.1.4 is that it's optional.  In your case,
> I'd calc 2,000 sf of dry system plus 1,900 sf of wet.  Since it's all light
> hazard, it shouldn't get ugly.
>
> I gotta believe there will be some tweaking to that section, though.  I
> read the ROP and ROC - Tracey's 480 sf canopy (page 88 of the ROC) is
> probably being protected by 4 sprinklers, but could require a 4" supply
> pipe & dry valve since the phantom flow is added at the end of the dry
> x-main.  That doesn't seem reasonable to me.
>
> Ed Kramer
> Lawrence, KS
>
>
>
> > -----Original Message-----
> > From: [email protected] [mailto:sprinklerforum-
> > [email protected]] On Behalf Of Cahill, Christopher
> > Sent: Wednesday, March 13, 2013 4:46 PM
> > To: [email protected]
> > Subject: Phantom Flow
> >
> > Not what you think by the subject.  Working out of NFPA 13 '13
> > 23.4.4.1.1.5.  This is new and confusing us greatly.
> >
> > I have a 20,000 sq.ft. heated LH building. And a 2,000 sq.ft. area
> > that needs a dry system.  Not an auxiliary dry system.  My starting
> > required design is  0.1/3,900.  I calc the system at 2,000 sq.ft. (cuz
> > that's all I have) and get for discussion sake 220 gpm.  Then I
> > subtract from 390
> > (3,900 x 0.1 per 23.4.4.1.1.5) and I get 170 gpm.  Then I go back to
> > the calc and redo but this time I add 170 at the end of the main.  Now
> > this has the effect of overflowing all the rest of the BL's such my
> > final calc is more than 390.
> >
> > !@#$^#
> >
> > What if I have a 500 sq.ft. building and the next building is 20 miles
> > away  @#$@# are we calc'ing this extra area for?
> >
> > Can someone 'splain if we got it right and then why in the world this
> > got into the standard?
> >
> > Chris Cahill, PE*
> > Senior Fire Protection Engineer, Aviation & Facilities Group Burns &
> > McDonnell
> > 8201 Norman Center Drive
> > Bloomington, MN 55437
> > Phone:  952.656.3652
> > Fax:  952.229.2923
> > [email protected]<mailto:[email protected]>
> > www.burnsmcd.com<http://www.burnsmcd.com/>
> >
> > Proud to be one of FORTUNE's 100 Best Companies to Work For
> > *Registered
> > in: MN
> >
> >
> >
> >
> > -------------- next part -------------- An HTML attachment was
> > scrubbed...
> > URL:
> > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> > ch ments/20130313/26a3e378/attachment.html>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130314/ead3dbe9/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130314/cc5662f0/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to