What is your MSDS tell you, all of the chemicals in your list are either toxic 
and/or non-flammable, why the Class 1 Div 2?

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, March 18, 2013 9:46 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

I wasn't told this building had any classification until the questions came 
from the electrical contractor. The building is a Nitric Acid Plant, and the 
MSDS they gave me was for Nitrogen, Nitric Oxyde, Nitrogen Dioxyde and Oxygen. 
They have to sort out whether this building is classified class 1
div.2 as per the electrical code. If it is, the riser still has to be within 
the building, but the devices will have to comply with the electrical code.

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: March 18, 2013 9:51 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

Could ya enlighten us why you have a riser in a classified area?  Can be done 
but highly unusual, no?

And what's with the removal of brass?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, March 18, 2013 10:45 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

Thanks John and thanks to everyone that replied. I'm enlightened.

Tony 

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected] <[email protected]>
Sent: Sun Mar 17 00:24:00 2013
Subject: Sprinkler Tree

I had an electrical contractor commenting on a sprinkler tree, as following:

"The tamper switch and low flow switch are not rated for Class 1 Division 2 
applications. Also, the brass body valve and gauges should also be replaced".

Anyone know what he is talking about?

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to