Yeah, and what about it in relation to electrically classifying an area?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fairchild, Jack
Sent: Tuesday, March 19, 2013 12:25 PM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

I realize this is tongue in cheek, but you may want to check out section 3007.1 
of the 2009 IFC.

Jack Fairchild

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, March 19, 2013 11:59 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

B-b-but this project does have that dangerous nitrogen gas!

Had someone get all excited on a recent project because of nitrogen and argon 
and started down this same trail of great alarm and concern.  It was kind of 
funny until I mentioned that neither were flammable or combustible.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Tuesday, March 19, 2013 11:19 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

Oxygen is an oxidizer all the other chemicals are toxic or acids, if you look 
up the requirements for hazardous areas as per NFPA 70 The National Electric 
code you will find no requirement for explosion proof electrical equipment 
someone is trying to confuse the issue and get the architect or Engineer to 
sign off on requiring explosion proof electrical equipment as a change order. 
We just had a mechanical engineer PE no less who required explosion proof 
electrical equipment in a oxygen gas manifold room of concrete construction and 
no fuel load, he even wanted to have combustible gas detectors installed, he 
insisted that because he was the mechanical engineer he was defining what was 
required after the project was bid out and he was making changes during 
material & equipment submittal process. The Owner finally stood up to the 
engineer and demanded that the engineer show him where in the code this type of 
explosion proof equipment was required. The engineer could not find any 
requirement in any code for the explosion proof equipment. The Owner 
back-charged the Engineering firm for the cost incurred and delay in 
construction because of his demands for a requirement that the engineer made 
up. 

Have a fire safe day!

Regards     

Jim

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, March 18, 2013 1:01 PM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

I wasn't told this building had any classification until the questions came 
from the electrical contractor. The building is a Nitric Acid Plant, and the 
MSDS they gave me was for Nitrogen, Nitric Oxyde, Nitrogen Dioxyde and Oxygen. 
They have to sort out whether this building is classified class 1
div.2 as per the electrical code. If it is, the riser still has to be within 
the building, but the devices will have to comply with the electrical code.

Tony   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: March 18, 2013 9:51 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

Could ya enlighten us why you have a riser in a classified area?  Can be done 
but highly unusual, no?

And what's with the removal of brass?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, March 18, 2013 10:45 AM
To: [email protected]
Subject: RE: Sprinkler Tree - Code Path

Thanks John and thanks to everyone that replied. I'm enlightened.

Tony 

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected] <[email protected]>
Sent: Sun Mar 17 00:24:00 2013
Subject: Sprinkler Tree

I had an electrical contractor commenting on a sprinkler tree, as following:

"The tamper switch and low flow switch are not rated for Class 1 Division 2 
applications. Also, the brass body valve and gauges should also be replaced".

Anyone know what he is talking about?

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to