Now I get it.  So go to the Chapter 5 table in the Building Code on required 
separation of occupancies.   You have to separate your A4 courts from your B 
everything else with two hours if you're not sprinklered, correct?  If there 
are any other uses in the building, you'll want the client to pencil that out 
and that's when the a-ha moment likely occurs regarding sprinklers.   Not sure 
how much of this is IBC and how much is California amendment, but 903.2.1.4 of 
the 2010 CBC says that sprinklers are required in A4 when the fire area exceeds 
12,000 sq. ft.; when the area has an occupant load of 300 or more; where the 
fire are is located on a floor other than a level of exit discharge.   So if 
the two hours don't get 'em then the area limit or weird exterior stairs at a 
two-story health or fitness club likely will.   

Steve 




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 21, 2013 3:50 PM
To: [email protected]
Subject: Re: Racquet Ball Court

2003 IFC 903.2.1.4 Group A-4.
An automatic sprinkler system shall be provided for Group A-4 occupancies where 
one or more of the following conditions exists:  
1.
2.
3.

Exception: Areas used exclusively as participant sports areas where the main 
floor area is located at the same level as the level of the exit discharge of 
the main entrance and exit. 

This exception has been deleted from all later versions on the code. 

----- Original Message -----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, March 21, 2013 10:39 PM
To: [email protected] <[email protected]>
Subject: RE: Racquet Ball Court

I only have 2006 IFC, and there is no 9504, nor corresponding section if I move 
the decimal point. Can you double check the section no. or post the section? 

Steve  




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 21, 2013 3:14 PM
To: [email protected]
Subject: RE: Racquet Ball Court

Tell me what is the intent of the exception  to IFC 2003 9054.3.2.1.4


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, March 21, 2013 2:57 PM
To: [email protected]
Subject: RE: Racquet Ball Court

And if the building is framed of wood?   Or has accessory (and fire loaded) 
occupancies?   How do we justify sending fire fighters toward or into a 
building subject to complete structural involvement in a fire that started in 
the rag pile that's kept in the shed adjacent to the outside of the buildings?

And methinks you're projecting on the concrete box/plaster lid scenario.   This 
thread didn't speak to that kind of construction and nearly every single 
building I've ever seen housing this use has been wood/Type V.   Possibly every 
single one, but I am admittedly in an area that doesn't require wind and snow 
loading or the R-values associated with concrete boxes and plaster ceilings ...

SML

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 21, 2013 2:49 PM
To: [email protected]
Subject: RE: Racquet Ball Court

Nope, it's the sprinkler forum, where we justify putting sprinklers over a 
swimming pool because they could drain the pool and fill it with pallets of 
class IV in racks! And  where we believe we should put sprinklers beneath a 
3'-11" metal canopy over the dock doors, on the outside of a building to keep a 
fire from getting inside, and as I check the 2009 IFC, it appears that we now 
believe it is completely necessary to install sprinklers in a concrete box with 
a plaster ceiling in which the only combustible material is the players, and 
the ball!?! And please don't misunderstand my motive, I have made my livelihood 
in the sprinkler industry for 37 years, but I am always opposed to spending 
anyone's money on so called fire protection the provides  no measurable benefit!
Mark at Aero

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, March 21, 2013 8:22 AM
To: [email protected]
Subject: RE: Racquet Ball Court

How many buildings out there exclusively contain sports courts?  Last I checked 
they all include are offices, locker rooms, fitness and exercise rooms, 
mechanical and equipment rooms, etc.

I had to double check that I wasn't subscribed to the BOMA Forum ...

SML




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 21, 2013 4:19 AM
To: [email protected]
Subject: Re: Racquet Ball Court

I believe Scot has a legitimate point here with the exception that there is 
already precedence in one or more of the Model Codes for the omission of 
sprinklers in these facilities. I recall that there are several qualifications 
required, that the sport venue be located on the ground floor with proper exits 
to outside, and the building be of Type III (non-combustable) construction. So 
possible the solutions should consider removal of the sprinklers. 
Mark at Aero 

----- Original Message -----
From: å... .... [mailto:[email protected]]
Sent: Thursday, March 21, 2013 09:36 AM
To: [email protected] <[email protected]>
Subject: Racquet Ball Court

How about getting stakeholders to consider whether NO sprinklers will be 
installed in the racquetball court based on the

   1.  low, if not insubstantial, fire loading in these rooms,
   2. low frequency of fire ignition in these rooms?

Prescriptions are prescriptions, and only on extenuating and justifiable 
circumstances are we allowed to invoke common sense to make an intervention.  
Someone, somewhere in the ladder of command, is paid good money for making 
decisions; should we not ask them (all of them) to
quantify items # 1. and # 2?   By putting  numbers on them (these two
items), we may evaluate our judgment as to "the need to sprinkler inside 
racquetball courts."

Is asking to evaluate a life safety judgment too controversial, too critical 
and perceived as too personal of a nature?  Is asking to evaluate a decision 
too much a cost imposition on a salaried vocation?  The end goal, is to provide 
better service to the public and users of these courts through reasonable and 
appropriate judgment, with a collateral benefit of benefiting future judgment 
through the examination of details in the current and past decisions.

It seems to be,  that presently, fires starting from inside a racquetball court 
have more import than fires starting in, say...many of the homes and dwellings 
where we sleep.  Realizing that we in design & installation are but one of the 
last links in the chain-of-events occurring when a decision is made to include 
fire sprinklers,  we might still pause to consider whether those making the 
first links would do better to offer the numbers behind their "good judgment", 
and state how, where and whether they come together to decide their Go/No-Go 
decision.


Scot Deal
Excelsior Fire/Risk Engineering
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130321/04fcea8d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to