See NFPA 20:Table 4.26 for test header requirements.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Easter, Timothy [mailto:[email protected]] 
Sent: Friday, March 29, 2013 11:58 AM
To: [email protected]
Subject: determining number of outlets for test header

I am use to providing one 2 ½" connection for every 250 gpm of system demand.

I do not know where this requirement came from nor do I know of any 
requirement. Does anyone know of such a requirement?

Regards,

Timothy Easter
E.I.T.
Graduate Fire Protection Engineer
URS Corporation
11832 Rock Landing Drive Suite 306
Newport News, VA 23606
Direct: (757) 383-6217
[email protected]<mailto:[email protected]>

This e-mail and any attachments contain URS Corporation confidential 
information that may be proprietary or privileged. If you receive this message 
in error or are not the intended recipient, you should not retain, distribute, 
disclose or use any of this information and you should destroy the e-mail and 
any attachments or copies.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130329/4f685e89/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to