Back from the old days of a playpipe and tip and 250 being about max average
per stream, but still Code.
It's funny, now with 1.75" and 2" nozzles, we use about half to 2/3 of the
outlets.
I did a 2000 gpm pump with 3 lines this morning.  Talk about easy...

TD
GRS


That’s where I was going to send him - the question was for test header, I
didn't see where the backflow testing came in... if its for number of hose
valves on a test header, then what Duane said.

Bobby Gillett

See NFPA 20:Table 4.26 for test header requirements.

Duane Johnson, PE

I am use to providing one 2 ½" connection for every 250 gpm of system
demand.

I do not know where this requirement came from nor do I know of any
requirement. Does anyone know of such a requirement?

Regards,

Timothy Easter 