Jack -

A K factor (in sprinkler world) is an expression of the relationship
between pressure and discharge, as"

K is equal to the DISCHARGE / SQUARE ROOT of PRESSURE

Note that the formula is not based on actual square root, but on a log
of 1.54   Square root is accepted in place of 1.54.

That ana answere?



At 04:36 PM 5/3/2013, you wrote:
Here's a Friday question that was asked of me:  What's a K-Factor?

The Brock Hydraulics book states it is the discharge coefficient, but I can't find it in NFPA 13. Am I missing it?

Jack Fairchild
_______________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to