NFPA 101:30.3.4.2.3    In buildings protected throughout by an approved, 
supervised automatic sprinkler system in accordance with 30.3.5, required fire 
alarm systems shall be initiated upon operation of the automatic sprinkler 
system.

Someone will need to go through Section 30.3.4.3 for notification requirements 
as they very based on the number of dwelling units, building height, etc.

Ask for the code reference for the deficiency that is being noted. 

Here is the audibility requirement for sleeping areas:

NFPA 72: 18.4.5 Sleeping Area Requirements.   
18.4.5.1    Where audible appliances are installed to provide signals for 
sleeping areas, they shall have a sound level of at least 15 dB above the 
average ambient sound level or 5 dB above the maximum sound level having a 
duration of at least 60 seconds or a sound level of at least 75 dBA, whichever 
is greater, measured at the pillow level in the area required to be served by 
the system using the A-weighted scale (dBA).




Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Greg McGahan [mailto:[email protected]] 
Sent: Wednesday, May 29, 2013 8:31 AM
To: [email protected]
Subject: Re: 13R local alarm

mount it in the closet


On Wed, May 29, 2013 at 7:03 AM, Todd - Work <[email protected]> wrote:

> I was thinking that a 6" bell inside an apartment might be a little 
> overkill as well as obtrusive.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
>
> On May 29, 2013, at 7:24 AM, Greg McGahan <[email protected]> wrote:
>
> > I am not sure what you are referring to exactly, but we often use a 
> > flow switch wored to a 6" electric bell.
> >
> >
> > On Tue, May 28, 2013 at 10:24 PM, Todd - Work <[email protected]> wrote:
> >
> >> I have an FM that wants local alarms for a 13R system within each 
> >> unit
> (3
> >> family house). Any suggestions on a small wall mounted unit?
> >>
> >> Todd G Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> www.fpdc.com
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> >
> >
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to