Chris,

The commodity and storage arrangement (length, height, single, double, etc) 
would need to be evaluated. Next the sprinkler system would need to be 
hydraulically evaluated. At that point, you can determine if in rack sprinklers 
are required.

One independent rack can be sprinklered and it could possible be fed from the 
ceiling system. However, your post stated that this occurred in "a few areas". 
That needs to be better defined.

The issue on type of inspection has been well covered by others and I won't 
chime in on that.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On May 29, 2013, at 9:46 AM, "Fire Protection Services" 
<[email protected]> wrote:

> Forum,
> 
> 
> 
> I performed an Inspection a few days ago and the building is design as Ord2
> with the exception of the shipping area which is Class 3.
> 
> I noticed in a few areas they have installed on single rack against the
> outside wall with misc storage stacked at various heights.
> 
> I  have never seen one independent rack sprinklered but it looks like to me
> it should be.
> 
> Has anyone ran into this before? What did you do?
> 
> 
> 
> Thanks
> 
> 
> 
> Chris Payne
> 
> Fire Protection Services
> 
> Owensboro
> 
> 
> 