I don't think this is your problem. It's an alarm problem. You just need to provide a means to trigger an alarm. Hereabouts a normal is a fire alarm system in common areas with an attached peizo in each unit and local smoke alarms throughout the units. But I don't care about this as the sprinkie. I supply a means to alarm from a flow. The rest is someone else's work. Local exterior alarm is another thing altogether. Don't work too hard solving someone else's (usually the GC) problem.
On Wed, May 29, 2013 at 2:16 PM, Steve Leyton <[email protected]>wrote: > Last cycle, when we were discussing yet another proposal to require a > mandatory local waterflow alarm in 13D, I asked out loud why it would be > so difficult to do just as Todd's fire official directed, i.e. use the > smoke detector loop as an audible network. And the answer is as simple > as most of the other "gotcha's" in our business: These appliances > aren't listed as a audible alarm device. And how you power them with a > flow switch could vary from manufacturer to manufacturer, and many > likely can't be configured that way. > > If anyone out there knows of a listed combination smoke > detector/interior audible alarm device, please send me that info off > forum at your very earliest convenience. If such an item doesn't yet > exist, perhaps the good people at Potter or System Sensor or another > manufacturer will see a business opportunity ... > > > Steve Leyton > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > John Drucker - Home > Sent: Wednesday, May 29, 2013 2:08 PM > To: [email protected] > Subject: RE: 13R local alarm > > Todd, How old are the smoke alarms ?, at 10 yrs. their due for > replacement anyway. > > As I commented earlier, a prescriptive way to solve the issue. > > John Drucker, CET > Fire Protection Subcode Official > Fire / Building / Electrical Inspector > New Jersey > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > Todd - Work > Sent: Wednesday, May 29, 2013 4:25 PM > To: [email protected] > Subject: Re: 13R local alarm > > The FM asked for the sprinkler alarms to be connected to ring the smoke > detectors. I asked if a separate bell would be acceptable. The present > system is essentially residential hard wired smokes. I'm not sure if all > of the devices in each unit go off when one activates. There is no > annunciation. I don't think the detectors are wired to accept additional > input, so the entire system would have to be replaced if we have to > interconnect. Right now they are not being asked to upgrade the alarms > and this is not a town with a wimpy fire marshal. > > The alarm system is beyond my contract and the drawing notes state so. > That is a can of worms I will let someone else open. > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > > On May 29, 2013, at 3:07 PM, "Tom Duross" <[email protected]> wrote: > > > We had a local town home rule go into effect 15+ years ago requiring > > sprinklers in anything 3+ units "substantially" renovated but it > > forgot to mention annunciation (also forgot water supply). Many slick > > > property owners got together and sued and after the dust settled, it > > was decided to put an electric bell in the stair lobby or main lobby > > of each unit plus the outside. No formal fire alarm was required. > > I've done the accessory relay to wire a dry contact to a 3 wire 120 > > vac smoke circuit but it voids the listing of the smokes, or did (been > > > many years). > > These days Todd, I don't know how you could install a sprinkler system > > > under current MA code and not have to install a formal 72 FA. 3 units > > > or more requires supervision and central station in MA. > > TD > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of > > Mike Henke > > Sent: Wednesday, May 29, 2013 11:43 AM > > To: [email protected]; > > [email protected] > > Subject: RE: 13R local alarm > > > > It may be possible to activate both the smoke alarms and a separate > > waterflow alarm. > > The flowswitch should have 2 sets of contacts. > > One switch can activate a local alarm such as the 120 vac mini horn > > The other switch may be able to activate the smoke alarms. > > > > This would provide the additional signal for waterflow so it wouldn't > > be confused with burnt toast. > > > > You probably have to contact the detector manufacturer to see how and > > if the detectors can be activated from a separate switch. They may > > have a separate module for this. > > There are some products on the market for this such as Firex but I > > don't know if they universally work with all makes and models of smoke > alarms. > > There was also a carrier frequency device made by Cepco products for > this. > > > > Regards, > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler > .org > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler > .org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org