I would strongly caution against using this method for estimate calculations. 
(Without doing extensive testing to verify that it is accurate)

The D-W and H-W calculation methods are simply approximations of how fluids 
interact with themselves and the pipe they are in. The H-W equation and the 
K-factor concept are two VERY specialized cases that are intended only to 
describe warm water in pipes coming out of a smooth hole.

The k-factor only relates the ease with which water can escape a sprinkler. If 
you plug in a modified k-factor, you are still using H-W to describe how the 
fluid is moving through the pipes. The reason that you have to switch to the 
D-W equation is because H-W will give you the wrong answer. If you use a 
modified K factor with H-W (instead of D-W) the most likely outcome is a wrong 
answer - although maybe not the same wrong answer as before.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 



On Jun 11, 2013, at 7:52 AM, "Brad Casterline" <[email protected]> wrote:

> From NFPA 13-2007, 22.4.4.5.1, we are required to, among other things,
> adjust the K-Factor. 
> 
> Using  the Hazen-Williams friction formula, 62.4 lb/ft3 / 144 in2 = .433
> lb/in2/ft(h).
> 
> If we have an AF solution at 65.5 lb/ft3, / 144 = .455 lb/in2/ft(h).
> 
> If K=5.6, and we assume P=7 PSI.:
> 
> 7/.433=16.166 ft(h). 7/.455=15.385 ft(h).*
> 
> 15.385/16.166=.952. sqrt(.952)=.976, x 5.6 = 5.46.
> 
> There is a chart in 13 showing a 50% glycerin solution at about -10F
> weighing about 15% more than 100% water: 62.4 x 1.15 = 71.76.
> 71.76/144=.498. 7/.498=14.056 ft(h). 14.056/16.166=.869. sqrt(.869)=.932, x
> 5.6 = 5.22.
> 
> If I had to fab the pipe today and formalize the submittal tomorrow (after
> googling centipoises for several hours) I would calc it like it was 'all
> wet', using K=5.22.  
> 
> * converting PSI to feet of head(h) it is seen that the denser the solution,
> the 'shorter' it is. Since v=sqrt(2gh), the shorter it is the slower it is.
> Making the adjustment based on "h", we have to take the square root of the
> ratio, i.e., (K=Q/sqrtP). If adjusted based on velocity we would use the
> ratio itself (square feet=cubic feet per second divided by feet per second):
> sqrt(2*32.2*16.166)=32.266 ft/sec.
> 
> sqrt(2*32.2*15.385)=31.477 ft/sec.
> 
> 31.477/32.266=.976.
> 
> 
> 
> The above is simply the type of thing I enjoy doing and like to share,
> hoping it will cause no harm, to be taken or left as one sees fit.
> 
> 
> 
> thanks,
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org