Over the course of my career we have penetrated duct work with sprinkler piping 
countless times.  The key to avoiding the issues of condensation and noise as 
Tom and Mark alluded to is to sleeve the duct.  Drop a 1.25" or 1.5" piece of 
round duct (can be hard to find it that small), or conduit, or the flex ducting 
that is referred to as "rubber hose" in the HVAC biz, and then pipe through 
that.  Seal the penetration of the sleeve and you get a better fit and finish 
as far as noise-proofing.  

I can't recall ever dropping through a duct vertically, but horizontally is 
almost always viable.  The MEOR should do a quick look-see calc' to assure that 
there isn't excessive friction loss from the sleeve(s) in the stream.


Steve Leyton



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, June 12, 2013 9:48 AM
To: [email protected]
Subject: routing sprinkler pipe through a duct

Yeah you read that right.

I had a query regarding running a 1" sprinkler drop through a duct to provide 
sprinklers below.  The client is afraid that running the line beside the duct 
will look ugly and doesn't want to do that. 

The area does have a finished ceiling and the duct is exposed and extends to 
about 2ft below the ceiling.  Essentially the duct is similar to a soffit as 
far as obstruction rules are concerned.  The duct is just over 48" in width.

I suggested just spacing the sprinklers beside the run of duct as if you were 
dealing with a soffit but for some reason the idea of punching through the duct 
is more attractive.

I couldn't find any prohibitive language in NFPA 13 that would prevent this.

Anyone know of anything or any text that expressly prohibits this?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to