Timothy,

Adding a floor drain into a space like a data center can have affects
beyond what you might think.  First, you need to have a trap primer system
(in a space such as this it would be an electrical type) in order to add
water to the trap so it doesn't dry out and introduce sewer gases to the
space.  Adding the water into the area will most likely require a
monitoring system to detect water leakage since that is detrimental to a
space such as this.  But the plumbing guy might have had to add some sort
of drain for the condensate from the a/c units and a cold water line for
the humidifier makeup.

So, let the plumber figure out if he needs a drain and water..  :-)

Richard



On Tue, Jun 18, 2013 at 10:08 AM, Easter, Timothy <[email protected]>wrote:

> For example in data centers, I thought it would be a good idea to have
> floor drains (under raised floors) installed for water removal upon
> sprinkler discharge. However, I was told no requirement exist. Does a
> requirement exist that I can't find. Thanks.
> Regards,
>
> Timothy Easter
> E.I.T.
> Graduate Fire Protection Engineer
> URS Corporation
>
>
>
> This e-mail and any attachments contain URS Corporation confidential
> information that may be proprietary or privileged. If you receive this
> message in error or are not the intended recipient, you should not retain,
> distribute, disclose or use any of this information and you should destroy
> the e-mail and any attachments or copies.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to