Subject: RE: air test for open head deluge system

Deluge systems are hydro tested just like any other sprinkler system except the 
outlets are plugged for the test.  After the test the plugs are removed and the 
spray nozzles are installed, or they can be pneumatically tested at 40 psi as 
stated on the Contractor's Material and Test Certificate for Aboveground 
Systems which appears in NFPA 13.

If he has a dry pilot actuation system, he may be referring to that for a 
pneumatic test as well, or for both systems.

Foam systems have their own set of tests as do deluge systems when it comes to 
verifying coverage and impingement on vessels.  See NFPA 16 for foam-water 
systems.

I would not blow air through the system to check for "bugs".  It should be 
flushed per NPFA procedures.

These kinds of statements don't exude a lot of confidence.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Friday, June 21, 2013 3:05 PM
To: [email protected]
Subject: air test for open head deluge system

I have a owner calling me because another contractor is stating that he needs 
to have an air test done on his open head foam deluge system.  

I have never heard of this and was wondering  what the test entails.
Any takers?

Thanks,

 

Dewayne Martinez

Fire Protection Design Manager

Total Mechanical

414-406-5208 (c) 262-522-7110 (w) 262-522-1006 (f)

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to