-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, June 24, 2013 8:29 AM To: [email protected] Subject: RE: air test for open head deluge system Deluge systems are hydro tested just like any other sprinkler system except the outlets are plugged for the test. After the test the plugs are removed and the spray nozzles are installed, or they can be pneumatically tested at 40 psi as stated on the Contractor's Material and Test Certificate for Aboveground Systems which appears in NFPA 13. If he has a dry pilot actuation system, he may be referring to that for a pneumatic test as well, or for both systems. Foam systems have their own set of tests as do deluge systems when it comes to verifying coverage and impingement on vessels. See NFPA 16 for foam-water systems. I would not blow air through the system to check for "bugs". It should be flushed per NPFA procedures. These kinds of statements don't exude a lot of confidence. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Martinez, Dewayne Sent: Friday, June 21, 2013 3:05 PM To: [email protected] Subject: air test for open head deluge system I have a owner calling me because another contractor is stating that he needs to have an air test done on his open head foam deluge system. I have never heard of this and was wondering what the test entails. Any takers? Thanks, Dewayne Martinez Fire Protection Design Manager Total Mechanical 414-406-5208 (c) 262-522-7110 (w) 262-522-1006 (f) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org