Hello,

We have an existing system installed 20 x 20 with 14.5K ECOH sprinklers. They 
have now installed  a new wall separating the space into 2 spaces and left the 
sprinklers overspaced off the wall. The Calc plate indicates that the design 
was originally .15 fpm over 2,000 soft  and when we re-calc the system we are 
nearly identical to the results recorded on the data plate. If we calculate it 
at .20/1,500 it does not work. 

Question is how to we even begin to sort this out in order to add a row of new 
heads to correct the overspacing? The new sprinklers all seem to be 
specifically listed for .20 (OH2) and i do not see a loophole to utilize a 
lower density and a larger Remote Area as in the original design. I also do not 
see an allowance in 13 for such a scenario (similar to the allowance for 
modifications to existing systems with residential heads that were originally 
designed for less than 7 psi end head pressure)

I do not think there will be any salvaging this system if we cannot reduce the 
density…

Thanks for any help,
Greg