Are you using a specific manufacturer sprinkler?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Jun 29, 2013, at 11:16 PM, Greg McGahan <[email protected]> wrote:

> Hello,
> 
> We have an existing system installed 20 x 20 with 14.5K ECOH sprinklers. They 
> have now installed  a new wall separating the space into 2 spaces and left 
> the sprinklers overspaced off the wall. The Calc plate indicates that the 
> design was originally .15 fpm over 2,000 soft  and when we re-calc the system 
> we are nearly identical to the results recorded on the data plate. If we 
> calculate it at .20/1,500 it does not work. 
> 
> Question is how to we even begin to sort this out in order to add a row of 
> new heads to correct the overspacing? The new sprinklers all seem to be 
> specifically listed for .20 (OH2) and i do not see a loophole to utilize a 
> lower density and a larger Remote Area as in the original design. I also do 
> not see an allowance in 13 for such a scenario (similar to the allowance for 
> modifications to existing systems with residential heads that were originally 
> designed for less than 7 psi end head pressure)
> 
> I do not think there will be any salvaging this system if we cannot reduce 
> the density…
> 
> Thanks for any help,
> Greg
> 