Do you need to call the AHJ?
If so I would just explain the situation as you did here and ask what they want 
the pressure regulated to. 

Forest Wilson

Sent from my iPhone

On Jul 7, 2013, at 12:32 PM, "Tom Duross" <[email protected]> wrote:

> Early post for the upcoming week.
> 
> I have a system to test, circa late 70’s installation.  Class 3 (assumed), 2
> ½” FDV’s with 1 ½” reducers and caps.
> 
> 
> 
> According to #25 the system should be tested to the appropriate standard it
> was installed under.
> 
> This all make perfect sense, some digging is required on my end as to what
> (if any) edition of #14 was in place at the time of installation.  My
> question is more towards the devices installed.
> 
> The system has older FDV’s cast saying Pressure Reducing Valve.  They’re the
> type with the locking clip on the handle stem that keeps the valve from
> being opened to a certain %.  Most of us know these are no more Pressure
> Reducing Valves than a standard angle type hose valves available yesterday
> or today.
> 
> There’s 90 PSI at the top of the standpipe, gauge looks accurate, drops when
> petcock is closed and the gauge is loosened.  Standpipe is 4” and runs up 8
> stories.  So I’m assuming around 140 PSI of the building’s fire pump as
> system pressure there.  Under 175 anyway.  Pretty sure 140% was the FP rule
> then, so 90-65 would seem in the range of design.  No drain risers btw.
> 
> 
> 
> Because these valves are labeled as PRV’s, I have to test everyone.  Now, I
> do have to check for the applicable edition of #14 and also the applicable
> Building Code because they sometimes have specific verbage for standpipes
> that could trump #14.  If I find no specific direction in either the Code or
> Standard requiring these, and I find for example the Code required 500@65
> for a design; I’m wondering how to approach the AHJ in requesting I remove
> and replace them with standard FDV’s off the shelf.
> 
> 
> 
> Some are missing their pins, some the locking screws are gone too.
> Installing standard valves would save testing 8 floors of FDV’s from now on,
> maybe improve outlet flow.  Any thoughts.
> 
> RIP GLC,
> 
> Thomas Duross
> 
> The Fire Pump Testing Company
> 
> 11 Varney Street
> 
> Jamaica Plain, MA 02130
> 
> T 617-971-0700
> 
> F 617-524-7171
> 
> C 617-592-4236
> 
> [email protected]
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to