Mike
The 2013 edition of NFPA 13 has clarified that this is acceptable.

6.3.1.1.1* Underground pipe shall be permitted to extend
into the building through the slab or wall not more than 24 in.
(0.6 m).

A.6.3.1.1.1 Extending the underground pipe into a building
provides working room to transition to the appropriate aboveground
piping. Environmental conditions should be considered
as outlined in 24.1.6.1.2.

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



Celebrating over 34 years of life safety

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim 
Davidson
Sent: Wednesday, July 10, 2013 9:10 AM
To: [email protected]
Subject: RE: Underground Stub-Up

Mike,

It is my understanding that the HDPE AWWA C906 pipe is not listed for use above 
ground and the transition from underground to above ground should be made with 
a DI Class 52 Flange spigot piece with rodding and thrust blocks. 

Have seen some very large dollar losses where the underground plastic pipe was 
exposed aboveground (about 6 inches above slab), and was damaged during the 
pouring of the floor slab or by physical contact. The installation was 
probability by an underground contractor with no knowledge of the UL and NFPA 
requirements. As the sprinkler contractor connecting on to the HDPF stub up you 
are assuming some liability since you have not informed the GC, CM, Owner of 
the problem in writing. Since the HDPE pipe stub up is before any water flow 
device a break at the above ground portion of the HDPE pipe can result in a 
large amount of water flowing before the break is detected.  

Have a fire safe day.

Jim 


  

DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike 
Hairfield
Sent: Wednesday, July 10, 2013 8:46 AM
To: AFSA SprinklerFORUM
Subject: Underground Stub-Up

Got a project that HDPE AWWA C906  pipe and fittings were installed.

 

The stub-up through the floor is a piece of HDPE AWWA C906 pipe with

a cap fused on the end and not rodded.

 

I've never seen this done before, is it acceptable with NFPA #24?

 

Mike Hairfield
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to