I revert to my question: If the FDC is for sprinklers only (not a
sprinkler/standpipe combo) has any fire guy reading ever pumped into one?
If a valve were closed or a line break in the lead-in would you pump into
one or direct all water from the pumper to hose lines? Is using, not just
hooking-up to, the FDC a standard fire-ground tactic?

"Representatives and direct Taxes shall be apportioned among the several
States which may be included within this Union, according to their
respective Numbers, which shall be *determined by adding to the whole
Number of free Persons, including **those bound to Service for a Term of
Years, and excluding Indians not taxed, **three fifths of all other Persons*
." Article 1, Section 2, Paragraph 3 of the United States
Constitution<http://en.wikipedia.org/wiki/United_States_Constitution>

Still there but pretty much just ink on paper.


On Fri, Jul 12, 2013 at 7:25 AM, <[email protected]> wrote:

> But what if the underground is a loop and has section valves plus the
> riser valves? The Phoenix Fire Dept. makes us put a FDC on each manifold
> instead of at the fire pump. The pump supplies the underground loop for the
> entire building with multiple lead ins. There are sectional gate valves in
> the loop, there is a gate valve in each underground leadin, and there are
> gate valves in each riser on a manifold. Phoenix says we can't have any
> gate valves between the FDC and the "system" gate valves. They read
> 8.17.2.4.3 and stop there. As far as the PFD is concerned 8.17.2.4.4
> doesn't apply.
>
> What do you guys think? Can there be multiple gate valves between the FDC
> and sprinkler systems?
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Charles
> Thurston
> Sent: Thursday, July 11, 2013 3:27 PM
> To: [email protected]
> Subject: Re: FDC Arrangement
>
> Hello All,
>
> I tend to use these for these situations  8.17.2.4.4 is the key to them.
>
> 8.17.2.4.2   For single systems, the fire department connection shall be
> installed  as follows:
>
> (1)  Wet system - on the system side of system control, check, and alarm
> valves (see Figure A.8.16.1.1)
> (2)  Dry system - between  the  system control valve and  the dry pipe
> valve
> (3)  Preaction system - between  the preaction valve and the check valve
> on the system side of the preaction valve
> (4)  Deluge system - on the system side of the deluge  valve
>
> 8.17.2.4.3   For multiple systems, the fire department connection shall be
> connected between
> the supply control valves and the system control valves.
>
> 8.17.2.4.4* The requirements of 8.17.2.4.2 and 8.17.2.4.3 shall not apply
> where the fire department connection is connected to the underground piping.
>
>
>
>
>
>
> --
> Best regards,
>  Charles                            mailto:[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to