I would be careful using a wet system even if it is called a "cooler". The 
evaporation coils can blow out air that is below freezing in order to get the 
whole cooler down to its target temp.

Also- just because they say they will keep it at 41 does not mean that they 
won't change their mind after it has been installed and dial it down.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Friday, July 12, 2013 10:34 AM
To: [email protected]
Subject: RE: dry pnds off dry system

The building footprint is 3800sf so I could eliminate a control valve
and a main by staying all dry.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, July 12, 2013 10:12 AM
To: [email protected]
Subject: RE: dry pnds off dry system

If it's a "cooler" and not subject to freezing you can put a wet system
in it.

Ron F

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Friday, July 12, 2013 8:15 AM
To: [email protected]
Subject: dry pnds off dry system

I have a small building which has both unheated / heated spaces.  I am
going to run the entire building as a dry system with standard pnd heads
on return bends in the heated areas with ceilings.  There is a cooler in
the heated area that will need sprinkler protection in.  Can I still put
standard pnds on return bends (in the heated area) for the cooler or do
I need to drop dry pnds?

Thanks,

Dewayne   

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to