That's very cool lol

But definitely this is one for me to remember when the next project comes up.

And it not varying more than 1 degree even in front of the blowers? Definitely 
interesting and as I said something to remember for the future.

Thanks Ron!

On Jul 12, 2013, at 11:33 PM, [email protected] wrote:

> We did a 40,000 sqft 36F beer cooler with a 44 ft high ceiling and used wet 
> ESFR's. The AHJ (Phoenix) was concerned about freezing so after the cooler 
> was up and running we put in a half dozen temperature recorders some in front 
> of blowers, some 20 ft above the floor, 6 ft off the floor at ceiling, well 
> you get the idea. After a week of recording temps every 5 minutes the results 
> were pretty amazing. Nothing varied more than 1 degree, usually less than .5.
> 
> Ron F
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of ampeck
> Sent: Friday, July 12, 2013 9:26 AM
> To: [email protected]
> Subject: Re: dry pnds off dry system
> 
> Ron that is kinda interesting, making me think.
> 
> Of course cold air falls and hot air rises so unless a sprinkler line is 
> close, depending on many factors, to the units the air is always going to be 
> warmer at the roof where the sprinkler pipe is at. I think most everyone(the 
> sales guys I've dealt with), just to err on the side of safety, says if it 
> says <40 you put in a dry or preaction system or use dry pendents is a small 
> cooler. I would assume if a cooler was 34F the unit has to be of producing 
> colder than 34F to maintain it. Depends of the BTU output and the placement 
> of piping in relation to the unit I would assume.
> 
> But most of my experience has been with large warehouses. And as far as BTU 
> output it can take a long time to bring those coolers, mine have being 
> larger, down to temperature. Like a week or so, but I don't know really 
> what's all involved in starting those system and the process.
> 
> I have to look this up but what can cause ice build up faster, with the 
> temperature hovering around freezing. Water filled pipe or dry system with 
> humidity in the air.
> I would say humidity in the air from a air dryer not working correctly is 
> worse. But I haven't thought about it until now. In water filled pipe the 
> unit has to bring the temperature of the surrounding water down enough to 
> freeze.
> 
> Nothing new to add just wanted to say your email just sparked my curiosity 
> about this.
> 
> Aaron P
> 
> On Jul 12, 2013, at 10:58 PM, [email protected] wrote:
> 
>> How many coolers can be turned into freezers using the same refrigeration 
>> equipment? The refrigeration units in coolers don't usually have the BTU 
>> capacity to bring the temp down to 28F and keep it there. We have installed 
>> hundreds of wet systems in 34F/35F coolers and have never had a freeze up. 
>> 13 says that it has to be below 40f "and" subject to freezing, it doesn't 
>> say "or" subject to freezing.
>> 
>> Ron F
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Matt 
>> Grise
>> Sent: Friday, July 12, 2013 8:39 AM
>> To: [email protected]
>> Subject: RE: dry pnds off dry system
>> 
>> I would be careful using a wet system even if it is called a "cooler". The 
>> evaporation coils can blow out air that is below freezing in order to get 
>> the whole cooler down to its target temp.
>> 
>> Also- just because they say they will keep it at 41 does not mean that they 
>> won't change their mind after it has been installed and dial it down.
>> 
>> Matt Grisé PE*, LEED AP, NICET II
>> Sales Engineer
>> Alliance Fire Protection
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>> 
>> *Licensed in KS & MO 
>> 
>> 913.888.0647 ph
>> 913.888.0618 f
>> 913.927.0222 cell
>> www. AFPsprink.com 
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> Martinez, Dewayne
>> Sent: Friday, July 12, 2013 10:34 AM
>> To: [email protected]
>> Subject: RE: dry pnds off dry system
>> 
>> The building footprint is 3800sf so I could eliminate a control valve and a 
>> main by staying all dry.
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> [email protected]
>> Sent: Friday, July 12, 2013 10:12 AM
>> To: [email protected]
>> Subject: RE: dry pnds off dry system
>> 
>> If it's a "cooler" and not subject to freezing you can put a wet system in 
>> it.
>> 
>> Ron F
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> Martinez, Dewayne
>> Sent: Friday, July 12, 2013 8:15 AM
>> To: [email protected]
>> Subject: dry pnds off dry system
>> 
>> I have a small building which has both unheated / heated spaces.  I am going 
>> to run the entire building as a dry system with standard pnd heads on return 
>> bends in the heated areas with ceilings.  There is a cooler in the heated 
>> area that will need sprinkler protection in.  Can I still put standard pnds 
>> on return bends (in the heated area) for the cooler or do I need to drop dry 
>> pnds?
>> 
>> Thanks,
>> 
>> Dewayne   
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to