Say the drop is 10 PSI:

10/.433=23.1 ft.(h)

v=(2gh)^.5=38.6 ft/sec

Area of 2" pipe=((2/24)^2)*PI=.0218 ft^2

38.6 ft/sec * .0218 ft^2 = .84 ft^3/sec, * 7.48 * 60 = 378 GPM.

 

This would be the maximum. It would less proportional to the friction head
loss.

If it is a short drop to a 90 and right out the wall maybe not too much Pf.

Regardless of any 'visual feel' one might get, if System Demand is 400 GPM,
one would have to go to plan B in this case.

 

thanks,

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 