There is a PI (Public Input) to Hanging and Bracing in regards to trapeze 
hangers. I am trying to get some information in regards to how other 
contractors are doing trapeze hangers and whether there have been issues. We 
primarily use angle iron when installing trapeze hangers. In that angle iron we 
have slots cut to attach to the bar joists. This is because the joists are 
never "perfectly" installed and the joists can be "wavy". We install the 
trapeze member with ATR, nuts and washers supported through the slot. I have 
pasted the PI language below.  Your opinions are welcome and will probably be 
used in the committee meeting.



9.1.1.7.7

Holes for bolts or rod shall not exceed 1⁄16 in. (1.6 mm) greater than the 
diameter of the bolt.



Statement of Problem and Substantiation for Public Input

The referenced term bolt also applies to all thread rod used commonly to 
support fire sprinkler

piping. Slots in the trapeze member may weaken the member. Like fire to a 
structural member,

the size of the slot permitted? - "it depends" due to the number of variables. 
The permitted slot

size based upon the structural

member has not been verified prior the submission date of this public input.



Peter Schwab

VP of Purchasing & Engineering Technologies



Wayne Automatic Fire Sprinklers Inc.

222 Capitol Court

Ocoee, Fl 34761



Mobile: (407) 468-8248

Direct: (407) 877-5570

Fax: (407) 656-8026



www.waynefire.com







Celebrating over 34 years of life safety