Hello Tom,

Based on :
>> 9.1.1.7.7
>> 
>> Holes for bolts or rod shall not exceed 1⁄16 in. (1.6 mm) greater than the
>> diameter of the bolt.


MY opinion is that slots of any size more then 1/16" wider then the fastener 
are not allowed. We always field drill them to fit.

Monday, August 5, 2013, 8:13:15 AM, you wrote:


> Let me follow-up on Pete's message.  I'm the one that submitted
> that public input.  I'm looking for guidance for the permitted slot
> sizes in angles based on the section modulus.  I understand
> fabrication shops will slot angles for you from what I hear but I
> can't get my hands on the reference material for permitted slot
> sizes.  Other contractors were forced (probably by the AHJ) to have
> these engineered by a structural engineer based on the loading of
> the pipe and backed with a very thick washer.  

> I'm not a structural engineer, but I know slotting angles will
> lessen it's structural integrity.  How wide and long is too much?  I
> want the approach to slotting angles for trapeze members to be correct.

> What is the reference guide for slots in structural steel?

> I found some online information - everything on the internet is true, correct?

> Tom


> On Aug 2, 2013, at 8:24 PM, Ben Young <[email protected]> wrote:

>> Why don't you just attach beam clamps to the angle iron in all three points
>> of attachment?

>> Personally, I've always preferred pipe trapeze hangers since you always
>> have scraps of that laying around.  Just make sure you put some beam clamps
>> on the ends of the trapeze member so it can't slip out for any reason.


>> Benjamin Young


>> On Fri, Aug 2, 2013 at 8:31 PM, Pete Schwab <[email protected]> wrote:

>>> Group

>>> There is a PI (Public Input) to Hanging and Bracing in regards to trapeze
>>> hangers. I am trying to get some information in regards to how other
>>> contractors are doing trapeze hangers and whether there have been issues.
>>> We primarily use angle iron when installing trapeze hangers. In that angle
>>> iron we have slots cut to attach to the bar joists. This is because the
>>> joists are never "perfectly" installed and the joists can be "wavy". We
>>> install the trapeze member with ATR, nuts and washers supported through the
>>> slot. I have pasted the PI language below.  Your opinions are welcome and
>>> will probably be used in the committee meeting.



>>> 9.1.1.7.7

>>> Holes for bolts or rod shall not exceed 1⁄16 in. (1.6 mm) greater than the
>>> diameter of the bolt.



>>> Statement of Problem and Substantiation for Public Input

>>> The referenced term bolt also applies to all thread rod used commonly to
>>> support fire sprinkler

>>> piping. Slots in the trapeze member may weaken the member. Like fire to a
>>> structural member,

>>> the size of the slot permitted? - "it depends" due to the number of
>>> variables. The permitted slot

>>> size based upon the structural

>>> member has not been verified prior the submission date of this public
>>> input.



>>> Peter Schwab

>>> VP of Purchasing & Engineering Technologies



>>> Wayne Automatic Fire Sprinklers Inc.

>>> 222 Capitol Court

>>> Ocoee, Fl 34761



>>> Mobile: (407) 468-8248

>>> Direct: (407) 877-5570

>>> Fax: (407) 656-8026



>>> www.waynefire.com







>>> Celebrating over 34 years of life safety


>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]

>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-- 
Best regards,
 Charles                            mailto:[email protected]