If you're talking about the heads in a combustible concealed space, then no. 
You calculate only one level of sprinklers, whichever is the most demanding.



Sent from my Verizon Wireless 4G LTE DROID


Andrei Titel <[email protected]> wrote:

In an OH building, concealed sprinklers must be added to flow calculation?

In addition, for example,if I have 6 sprinklers on a branch, protecting the 
floor, can I use the same branch for connecting 6 concealed sprinklers?

Thank you