Is there a limitation in connecting 2 levels of sprinkler on the same branch 
line? 


________________________________
 From: Dale Wingard <[email protected]>
To: "[email protected]" 
<[email protected]> 
Sent: Saturday, August 3, 2013 2:41 PM
Subject: Re: Concealed sprinklers
 

If you're talking about the heads in a combustible concealed space, then no. 
You calculate only one level of sprinklers, whichever is the most demanding.



Sent from my Verizon Wireless 4G LTE DROID


Andrei Titel <[email protected]> wrote:

In an OH building, concealed sprinklers must be added to flow calculation?

In addition, for example,if I have 6 sprinklers on a branch, protecting the 
floor, can I use the same branch for connecting 6 concealed sprinklers?

Thank you