NFPA 13- 23.2.3.1.2 " Pressure tanks shall be provided with approved means for 
automatically maintaining the required air pressure"
NFPA 22 carries the full requirements.



C. Burton Ford
NICET Certified IV
NFPA Certified Fire Protection Specialist
Cintas Fire Protection Inc
1038 Conshohocken Rd
Conshohocken, PA 19428
Tel 610-233-1400
Fax 610-233-1401


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay Stough
Sent: Friday, August 09, 2013 8:11 AM
To: Sprinkler -Forum
Subject: Pressurized tanks

We did some service work at a building that has a pressurized tank for water 
supply.  This is the third time we went there that the air compressor to the 
tank was off.  The company that does the inspections happened to be there and 
my service guy asked why the compressor was off.  His response was that an 
engineer told him that after you pressurize the tank, you turn the compressor 
off.  I always thought that you keep the compressor on to maintain the tank 
pressure, similar to a dry system, to keep the pressure higher to push all the 
water out of the tank if you need the entire supply.   The compressor does have 
a pressure switch on it.

   Am I correct on this thinking or am I missing something?


Jay Stough, CET
Doylestown, PA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

This e-mail transmission contains information that is intended to be 
confidential and privileged. If you receive this e-mail and you are not a named 
addressee you are hereby notified that you are not authorized to read, print, 
retain, copy or disseminate this communication without the consent of the 
sender and that doing so is prohibited and may be unlawful. Please reply to the 
message immediately by informing the sender that the message was misdirected. 
After replying, please delete and otherwise erase it and any attachments from 
your computer system. Your assistance in correcting this error is appreciated.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to