1. Is there a list of chemicals and their quantities used or stored in the 
room?   The type of chemicals can have significant impact on the fire 
protection design, a lab handling water reactive chemicals for example or 
combustible metals or pyrophorics.   Know what you plan to put water on.

2. Are flammables/combustibles stored in the room or in fire rated cabinets?

3. Is there MSDS info on all chemicals?

4. Have all chemicals been found to be miscible or in limited or 
inconsequential quantities in order for water based sprinklers to be effective? 
 

5. Are there chemical fume hoods and exhaust ductwork that requires internal 
fire suppression systems or the extension of fire sprinklers within?

Step #1 when dealing with chemicals, know what you're dealing with.  The fire 
code deals with different hazards and materials, if you don't know what's in 
the room, you'll have no idea what chapter to start reading.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bob
Sent: Tuesday, September 03, 2013 2:47 PM
To: [email protected]
Subject: RE: Small Chemical Storage Room

My first thought as well.  I just received this, this morning.  Someone else 
did the design and installed it, now looking for justification for the AHJ.

Bob Knight, CET III
208-318-3057


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron 
Greenman
Sent: Tuesday, September 03, 2013 12:42 PM
To: [email protected]
Subject: Re: Small Chemical Storage Room

I think I'd think it through more if it was mine to do, but my first instinct 
would be to treat it like the paint mixing room typically attached to  spray 
booth. Then I'd ask what's it it. If a Gilbert Chemistry Set array of stuff 
then it's really nothing. If more exciting stuff then....


On Tue, Sep 3, 2013 at 11:28 AM, Bob <[email protected]> wrote:

> I have a project with a small chemical prep/storage room that is 253 
> sf (19'
> x 13'4).  NFPA 13 calls out chemical labs as OH2, but I can't find 
> anything about the storage/prep.  This is a community college science 
> lab.  What would be the appropriate design criteria for this room, or 
> what would be the proper code to reference?
>
> Thanks,
>
> Bob Knight, CET III
> 208-318-3057
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to