In Nashville two weeks ago the installation committee voted that if the sprinkler wasn't removed from the fitting it was installed into and was handled with care, then it could be reused (Remove the drop). Also, a dry sprinkler can be removed and then reinstalled provided the wrench was used on the barrel and not the sprinkler. However this has not been balloted officially so it could change. You will be able to submit comments on this matter next spring during the comment stage.
My opinion only and not that of NFPA. Peter Schwab VP of Purchasing & Engineering Technologies Wayne Automatic Fire Sprinklers Inc. 222 Capitol Court Ocoee, Fl 34761 Mobile: (407) 468-8248 Direct: (407) 877-5570 Fax: (407) 656-8026 www.waynefire.com Celebrating over 34 years of life safety -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brad Casterline Sent: Thursday, September 05, 2013 12:59 PM To: [email protected] Subject: RE: removing sprinkler on drop I can't imagine what the opinion of the marketing geniuses for head making companies would be ;) . I wonder if any were on a committee or two? -----Original Message----- From: Mike Hill [mailto:[email protected]] Sent: Thursday, September 05, 2013 11:53 AM To: [email protected] Subject: RE: removing sprinkler on drop NEW sprinklers are susceptible to damage in the back of the delivery truck on a hot summer afternoon. My gut tells me lawyers and insurance companies have annual meetings at the same time and in the same hotel. Mike Hill -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Thursday, September 05, 2013 12:19 PM To: [email protected] Subject: Re: removing sprinkler on drop H ave we sufficient evidence that it is the reinstalled heads are the ones accidently discharging? It just seems like a waste to throw a 20 dollar head away because you have to remove and reinstall.....or even a 3 dollar head. We WILL comply with code, but I strongly disagree. Greg On Thu, Sep 5, 2013 at 10:54 AM, Todd - Work <[email protected]> wrote: > I would think that the vast majority of problems in mis-handling > sprinklers in this manner come from premature actuation (especially > with glass bulb) and not failure to actuate in a fire. I would also > think that only in very rare circumstances would you lose a building > due to an accidental discharge of a sprinkler. > > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > > On Sep 5, 2013, at 11:48 AM, "Cahill, Christopher" > <[email protected]> > wrote: > > > "then it appears you can re-use sprinklers left in drops or sprigs" > Where does this appearance come from? I don't see it in the Code, > Annex or Handbook. Quite frankly, that is the only place that counts > in descending order of priority. > > > > I agree with Todd there is some judgment and risk tolerance. I'm > > sure > not 'buying' a building loss over what a <$10 device I my current role. > When I was a contractor maybe we weren't perfect in this regard. > When I was an AHJ if asked - new, and lot of don't ask don't tell. > > > > Chris Cahill, PE* > > Senior Fire Protection Engineer > > Burns & McDonnell > > 8201 Norman Center Drive > > Bloomington, MN 55437 > > Phone: 952.656.3652 > > Fax: 952.229.2923 > > [email protected] > > www.burnsmcd.com > > > > Proud to be one of FORTUNE's 100 Best Companies to Work For > > *Registered in: MN > > > > > > > > > > > > -----Original Message----- > > From: [email protected] [mailto: > [email protected]] On Behalf Of Mark A. > Sornsin, P.E. > > Sent: Thursday, September 05, 2013 10:27 AM > > To: [email protected] > > Subject: RE: removing sprinkler on drop > > > > I would argue that this shouldn't be an argument as long as it is > specified up-front. If the owner or engineer says do not reinstall, > then don't argue, because if you win, it is your butt on the line > should the head fail. > > > > If this is a competitive bid situation or direct work with owner, > > with > no c > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org