NEW sprinklers are susceptible to damage in the back of the delivery truck
on a hot summer afternoon.
My gut tells me lawyers and insurance companies have annual meetings at the
same time and in the same hotel.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Thursday, September 05, 2013 12:19 PM
To: [email protected]
Subject: Re: removing sprinkler on drop

H
ave we sufficient evidence that it is the reinstalled heads are the ones
accidently discharging?

It just seems like a waste to throw a 20 dollar head away because you have
to remove and reinstall.....or even a 3 dollar head.

We WILL comply with code, but I strongly disagree.

Greg



On Thu, Sep 5, 2013 at 10:54 AM, Todd - Work <[email protected]> wrote:

> I would think that the vast majority of problems in mis-handling 
> sprinklers in this manner come from premature actuation (especially 
> with glass bulb) and not failure to actuate in a fire. I would also 
> think that only in very rare circumstances would you lose a building 
> due to an accidental discharge of a sprinkler.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
>
> On Sep 5, 2013, at 11:48 AM, "Cahill, Christopher" 
> <[email protected]>
> wrote:
>
> > "then it appears you can re-use sprinklers left in drops or sprigs"
>  Where does this appearance come from?  I don't see it in the Code, 
> Annex or Handbook.  Quite frankly, that is the only place that counts 
> in descending order of priority.
> >
> > I agree with Todd there is some judgment and risk tolerance.  I'm 
> > sure
> not 'buying' a building loss over what a <$10 device I my current role.
>  When I was a contractor maybe we weren't perfect in this regard.  
> When I was an AHJ if asked - new, and lot of don't ask don't tell.
> >
> > Chris Cahill, PE*
> > Senior Fire Protection Engineer
> > Burns & McDonnell
> > 8201 Norman Center Drive
> > Bloomington, MN 55437
> > Phone:  952.656.3652
> > Fax:  952.229.2923
> > [email protected]
> > www.burnsmcd.com
> >
> > Proud to be one of FORTUNE's 100 Best Companies to Work For 
> > *Registered in: MN
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Mark A.
> Sornsin, P.E.
> > Sent: Thursday, September 05, 2013 10:27 AM
> > To: [email protected]
> > Subject: RE: removing sprinkler on drop
> >
> > I would argue that this shouldn't be an argument as long as it is
> specified up-front.  If the owner or engineer says do not reinstall, 
> then don't argue, because if you win, it is your butt on the line 
> should the head fail.
> >
> > If this is a competitive bid situation or direct work with owner, 
> > with
> no c
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________