The last section below is the most important in your case.

>From NFPA 25 (2011):
5.4.1.1   Replacement sprinklers shall have the proper characteristics for the 
application intended, which include the following:

    (1)    Style
    (2)    Orifice size and K-factor
    (3)    Temperature rating
    (4)    Coating, if any
    (5)    Deflector type (e.g., upright, pendent, sidewall)
    (6)    Design requirements

5.5 Component Action Requirements.
5.5.1    Whenever a component in a sprinkler system is adjusted, repaired, 
reconditioned, or replaced, the actions required in Table 5.5.1 shall be 
performed.
5.5.3    Where the original installation standard is different from the cited 
standard, the use of the appropriate installing standard shall be permitted.
5.5.4    These actions shall not require a design review, which is outside the 
scope of this standard.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Pete Schwab [mailto:[email protected]] 
Sent: Thursday, September 05, 2013 4:11 PM
To: [email protected]
Subject: RE: removing sprinkler on drop

Duane,
This is for additions or modifications. What about older systems with painted 
heads or having to remove a sprinkler for evaluation (20 Year testing 
requirement per NFPA 25). Manufacturer's no longer produce the sprinklers that 
used to have densities as low as .032. We have some areas where the AHJ's will 
require permitting to replace painted sprinklers. Then they require 
calculations using the new listed flows and pressures which means ripping pipe 
out. It is unreasonable but I am seeing it more and more.


Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



Celebrating over 34 years of life safety


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, 
Duane (NIH/OD/ORS) [C]
Sent: Thursday, September 05, 2013 3:43 PM
To: [email protected]
Subject: RE: removing sprinkler on drop

11.3.1.4 (2013)    For modifications or additions to existing systems equipped 
with residential sprinklers, the listed discharge criteria less than 0.1 
gpm/ft2 (4.1 mm/min) shall be permitted to be used.

I guess the trick is to get the old listing info from the mfg.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services National 
Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, September 05, 2013 3:06 PM
To: [email protected]
Subject: RE: removing sprinkler on drop

I dunno Pete - didn't we hear a proposal in that regard last week?  Who 
submitted that?

The FIRE CODE tells us that, absent a change of use and/or occupancy, a FLS 
system is required to be maintained in accordance with the code(s) and 
standard(s) that governed at the time the system and building were
originally permitted for occupancy.   So you would use your professional
judgment to select a new sprinkler that most closely approximates the discharge 
characteristics and RTI of the displaced sprinkler and move
on.     

This isn't rocket science.  Is there anyone who thinks that replacing a 
sprinkler with one of the same K-factor and RTI will compromise the capability 
of a control-mode system to function properly in that mode?
Regardless of whether that sprinkler is listed for .03 or .05 or is calculated 
at .10?

SML



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Pete Schwab
Sent: Thursday, September 05, 2013 11:56 AM
To: [email protected]
Subject: RE: removing sprinkler on drop

Steve
So what do you do if the sprinkler is no longer available? (Residential 
sprinklers prior to the minimum .05 density and the NFPA 13 2002 requirement 
for a minimum 0.10 density) Pete

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



Celebrating over 34 years of life safety


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Thursday, September 05, 2013 1:38 PM
To: [email protected]
Subject: RE: removing sprinkler on drop

I didn't mean it as a poke at you - this is the same underlying problem as with 
ITM.  So long as there are one or two service providers that will do an 
"inspection" for $250, then it's always going to be that much more challenging 
to sell a complete and comprehensive professional
service package into that market.   More universally, the standard
practice needs to be that sprinklers be replaced when they are removed from 
fittings, period.  And this will entail hammering on enforcers to hold up their 
end of the equation as well, which is really the only way
that unscrupulous corner-cutters can be held accountable.   

Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg 
McGahan
Sent: Thursday, September 05, 2013 10:30 AM
To: [email protected]
Subject: Re: removing sprinkler on drop

"adjust prices"
With all due respect Steve - I said the WE would comply with code......we are 
still in the fight every day with those that don't. So issues like this are 
business killers for those of us that work with the unscrupulous and 
uneducated....Not that we ourselves are unfallible - but we do at least try.


On Thu, Sep 5, 2013 at 11:28 AM, Steve Leyton
<[email protected]>wrote:

> I was asked about 4 years ago to assist with a lawsuit as either a 
> technical consultant or designated expert that was focused on this 
> exact issue.  The case was over a sprinkler that discharged in a
retail suite
> that was being remodeled.   A sprinkler contractor had relocated a
> sprinkler by wrenching out the drop with sprinkler intact, and 
> reinstalling it a couple feet away.  After they did the work, there 
> were painters and finishers working in the suite over a weekend.
> Sunday night, the sprinkler released and flooded the suite, wrecked 
> the new paint and drywall, etc., etc.
>
> Neither side could prove their points.  The sprinkie alleged that 
> other trades must have hit the pipe and the finishers and painters 
> were using pads and rollers on extensions, so that was a distinct
possibility.
> And there were teeth marks on the drop, but it wasn't possible to say 
> forensically and with certainty if they were made during the T.I. or 
> rough-in.  But, there was no way corroborate the fitter's affidavit
that
> he hadn't dropped, wrenched or mishandled the sprinkler.   No forensic
> conclusions could be reached regarding the sprinkler, as certain parts

> were missing and someone (a responding firefighter, allegedly) had 
> badly damaged the sprinkler.  The bottom line is that if the sprinkler

> had been new, there would have been no allegation of negligence 
> against the sprinkie.
>
> Whatever sprinklers cost, this is the new price of tea in China folks.
> Adjust prices and let's move on.
>
> Steve
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Greg McGahan
> Sent: Thursday, September 05, 2013 9:19 AM
> To: [email protected]
> Subject: Re: removing sprinkler on drop
>
> H
> ave we sufficient evidence that it is the reinstalled heads are the 
> ones accidently discharging?
>
> It just seems like a waste to throw a 20 dollar head away because you 
> have to remove and reinstall.....or even a 3 dollar head.
>
> We WILL comply with code, but I strongly disagree.
>
> Greg
>
>
>
> On Thu, Sep 5, 2013 at 10:54 AM, Todd - Work <[email protected]> wrote:
>
> > I would think that the vast majority of problems in mis-handling 
> > sprinklers in this manner come from premature actuation (especially 
> > with glass bulb) and not failure to actuate in a fire. I would also 
> > think that only in very rare circumstances would you lose a building

> > due to an accidental discharge of a sprinkler.
> >
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> >
> > On Sep 5, 2013, at 11:48 AM, "Cahill, Christopher"
> > <[email protected]>
> > wrote:
> >
> > > "then it appears you can re-use sprinklers left in drops or
sprigs"
> >  Where does this appearance come from?  I don't see it in the Code, 
> > Annex or Handbook.  Quite frankly, that is the only place that 
> > counts in descending order of priority.
> > >
> > > I agree with Todd there is some judgment and risk tolerance.  I'm 
> > > sure
> > not 'buying' a building loss over what a <$10 device I my current
> role.
> >  When I was a contractor maybe we weren't perfect in this regard.
> > When I was an AHJ if asked - new, and lot of don't ask don't tell.
> > >
> > > Chris Cahill, PE*
> > > Senior Fire Protection Engineer
> > > Burns & McDonnell
> > > 8201 Norman Center Drive
> > > Bloomington, MN 55437
> > > Phone:  952.656.3652
> > > Fax:  952.229.2923
> > > [email protected]
> > > www.burnsmcd.com
> > >
> > > Proud to be one of FORTUNE's 100 Best Companies to Work For 
> > > *Registered in: MN
> > >
> > >
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Mark A.
> > Sornsin, P.E.
> > > Sent: Thursday, September 05, 2013 10:27 AM
> > > To: [email protected]
> > > Subject: RE: removing sprinkler on drop
> > >
> > > I would argue that this shouldn't be an argument as long as it is
> > specified up-front.  If the owner or engineer says do not reinstall,

> > then don't argue, because if you win, it is your butt on the line 
> > should the head fail.
> > >
> > > If this is a competitive bid situation or direct work with owner, 
> > > with
> > no c
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to