And there, as Roland also points out over and over, is the crux of it all.
And not even a square hole, but a varying rectangular one at best, with
calculations containing numbers from constants (compromises to begin with),
to a fixed guesstimate of coefficients based on varying factors at a given
time somewhere in the future, to numbers gathered at a fixed point in time
from a variable system, by recording the average of a fluctuating gause.
Yep. I think four decimal places accuracy is necessary given those
conditions.


On Thu, Sep 5, 2013 at 6:02 PM, Todd Williams <[email protected]> wrote:

> If there was ever an application of putting a square peg (design spacing)
> in a round hole (actual discharge pattern), sprinklers is it.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080
> www.fpdc.com
>
>
> On Sep 5, 2013, at 5:31 PM, <[email protected]> wrote:
>
> > Do you mean the same rectangular spray pattern? ( hehe)
> >
> > Ron F
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> > Sent: Thursday, September 05, 2013 12:17 PM
> > To: [email protected]
> > Subject: RE: removing sprinkler on drop
> >
> > I still have fresh enough scars to throw SAME PATTERN in there too :)
> >
> > -----Original Message-----
> > From: Steve Leyton [mailto:[email protected]]
> > Sent: Thursday, September 05, 2013 2:06 PM
> > To: [email protected]
> > Subject: RE: removing sprinkler on drop
> >
> > I dunno Pete - didn't we hear a proposal in that regard last week?  Who
> submitted that?
> >
> > The FIRE CODE tells us that, absent a change of use and/or occupancy, a
> FLS system is required to be maintained in accordance with the code(s) and
> standard(s) that governed at the time the system and building were
> > originally permitted for occupancy.   So you would use your professional
> > judgment to select a new sprinkler that most closely approximates the
> discharge characteristics and RTI of the displaced sprinkler and move
> > on.
> >
> > This isn't rocket science.  Is there anyone who thinks that replacing a
> sprinkler with one of the same K-factor and RTI will compromise the
> capability of a control-mode system to function properly in that mode?
> > Regardless of whether that sprinkler is listed for .03 or .05 or is
> calculated at .10?
> >
> > SML
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> Pete Schwab
> > Sent: Thursday, September 05, 2013 11:56 AM
> > To: [email protected]
> > Subject: RE: removing sprinkler on drop
> >
> > Steve
> > So what do you do if the sprinkler is no longer available? (Residential
> sprinklers prior to the minimum .05 density and the NFPA 13 2002
> requirement for a minimum 0.10 density) Pete
> >
> > Peter Schwab
> > VP of Purchasing & Engineering Technologies
> >
> > Wayne Automatic Fire Sprinklers Inc.
> > 222 Capitol Court
> > Ocoee, Fl 34761
> >
> > Mobile: (407) 468-8248
> > Direct: (407) 877-5570
> > Fax: (407) 656-8026
> >
> > www.waynefire.com
> >
> >
> >
> > Celebrating over 34 years of life safety
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> Steve Leyton
> > Sent: Thursday, September 05, 2013 1:38 PM
> > To: [email protected]
> > Subject: RE: removing sprinkler on drop
> >
> > I didn't mean it as a poke at you - this is the same underlying problem
> as with ITM.  So long as there are one or two service providers that will
> do an "inspection" for $250, then it's always going to be that much more
> challenging to sell a complete and comprehensive professional
> > service package into that market.   More universally, the standard
> > practice needs to be that sprinklers be replaced when they are removed
> from fittings, period.  And this will entail hammering on enforcers to hold
> up their end of the equation as well, which is really the only way
> > that unscrupulous corner-cutters can be held accountable.
> >
> > Steve
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> Greg McGahan
> > Sent: Thursday, September 05, 2013 10:30 AM
> > To: [email protected]
> > Subject: Re: removing sprinkler on drop
> >
> > "adjust prices"
> > With all due respect Steve - I said the WE would comply with
> code......we are still in the fight every day with those that don't. So
> issues like this are business killers for those of us that work with the
> unscrupulous and uneducated....Not that we ourselves are unfallible - but
> we do at least try.
> >
> >
> > On Thu, Sep 5, 2013 at 11:28 AM, Steve Leyton
> > <[email protected]>wrote:
> >
> >> I was asked about 4 years ago to assist with a lawsuit as either a
> >> technical consultant or designated expert that was focused on this
> >> exact issue.  The case was over a sprinkler that discharged in a
> > retail suite
> >> that was being remodeled.   A sprinkler contractor had relocated a
> >> sprinkler by wrenching out the drop with sprinkler intact, and
> >> reinstalling it a couple feet away.  After they did the work, there
> >> were painters and finishers working in the suite over a weekend.
> >> Sunday night, the sprinkler released and flooded the suite, wrecked
> >> the new paint and drywall, etc., etc.
> >>
> >> Neither side could prove their points.  The sprinkie alleged that
> >> other trades must have hit the pipe and the finishers and painters
> >> were using pads and rollers on extensions, so that was a distinct
> > possibility.
> >> And there were teeth marks on the drop, but it wasn't possible to say
> >> forensically and with certainty if they were made during the T.I. or
> >> rough-in.  But, there was no way corroborate the fitter's affidavit
> > that
> >> he hadn't dropped, wrenched or mishandled the sprinkler.   No forensic
> >> conclusions could be reached regarding the sprinkler, as certain parts
> >
> >> were missing and someone (a responding firefighter, allegedly) had
> >> badly damaged the sprinkler.  The bottom line is that if the sprinkler
> >
> >> had been new, there would have been no allegation of negligence
> >> against the sprinkie.
> >>
> >> Whatever sprinklers cost, this is the new price of tea in China folks.
> >> Adjust prices and let's move on.
> >>
> >> Steve
> >>
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of
> >> Greg McGahan
> >> Sent: Thursday, September 05, 2013 9:19 AM
> >> To: [email protected]
> >> Subject: Re: removing sprinkler on drop
> >>
> >> H
> >> ave we sufficient evidence that it is the reinstalled heads are the
> >> ones accidently discharging?
> >>
> >> It just seems like a waste to throw a 20 dollar head away because you
> >> have to remove and reinstall.....or even a 3 dollar head.
> >>
> >> We WILL comply with code, but I strongly disagree.
> >>
> >> Greg
> >>
> >>
> >>
> >> On Thu, Sep 5, 2013 at 10:54 AM, Todd - Work <[email protected]> wrote:
> >>
> >>> I would think that the vast majority of problems in mis-handling
> >>> sprinklers in this manner come from premature actuation (especially
> >>> with glass bulb) and not failure to actuate in a fire. I would also
> >>> think that only in very rare circumstances would you lose a building
> >
> >>> due to an accidental discharge of a sprinkler.
> >>>
> >>> Todd G Williams, PE
> >>> Fire Protection Design/Consulting
> >>> Stonington, CT
> >>> www.fpdc.com
> >>>
> >>> On Sep 5, 2013, at 11:48 AM, "Cahill, Christopher"
> >>> <[email protected]>
> >>> wrote:
> >>>
> >>>> "then it appears you can re-use sprinklers left in drops or
> > sprigs"
> >>> Where does this appearance come from?  I don't see it in the Code,
> >>> Annex or Handbook.  Quite frankly, that is the only place that
> >>> counts in descending order of priority.
> >>>>
> >>>> I agree with Todd there is some judgment and risk tolerance.  I'm
> >>>> sure
> >>> not 'buying' a building loss over what a <$10 device I my current
> >> role.
> >>> When I was a contractor maybe we weren't perfect in this regard.
> >>> When I was an AHJ if asked - new, and lot of don't ask don't tell.
> >>>>
> >>>> Chris Cahill, PE*
> >>>> Senior Fire Protection Engineer
> >>>> Burns & McDonnell
> >>>> 8201 Norman Center Drive
> >>>> Bloomington, MN 55437
> >>>> Phone:  952.656.3652
> >>>> Fax:  952.229.2923
> >>>> [email protected]
> >>>> www.burnsmcd.com
> >>>>
> >>>> Proud to be one of FORTUNE's 100 Best Companies to Work For
> >>>> *Registered in: MN
> >>>>
> >>>>
> >>>>
> >>>>
> >>>>
> >>>> -----Original Message-----
> >>>> From: [email protected] [mailto:
> >>> [email protected]] On Behalf Of Mark A.
> >>> Sornsin, P.E.
> >>>> Sent: Thursday, September 05, 2013 10:27 AM
> >>>> To: [email protected]
> >>>> Subject: RE: removing sprinkler on drop
> >>>>
> >>>> I would argue that this shouldn't be an argument as long as it is
> >>> specified up-front.  If the owner or engineer says do not reinstall,
> >
> >>> then don't argue, because if you win, it is your butt on the line
> >>> should the head fail.
> >>>>
> >>>> If this is a competitive bid situation or direct work with owner,
> >>>> with
> >>> no c
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er.org
> >>
> >>
> >>
> >> --
> >> Greg McGahan
> >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> >> 1160 McKenzie Road
> >> Cantonment, FL 32533
> >> 850-937-1850
> >> fax 850-937-1852
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er
> >> .org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> >
> >
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to