What you have are standard ANSI flanges on your domestic (US) valves and 
fittings.  You can purchase ANSI/DIN flange adapters that have a relatively 
short takeout to remedy this issue.  This will preclude any warranty voidances 
and, unless you simply have no space, make for an easy install.  I have 
included a web link for your convenience, if you need further information 
please feel free to contact me at your leisure.  
http://catalog.ktronpremier.com/viewitems/flow-transition-adapters/round-aerolock-flange-to-din-ansi-flange-adapters

Best regards,

Chris Ice
Fire Protection & Industrial Consultant
Hajoca Corporation
1418 Fruitville Pike
Lancaster, Pa. 17601
717-770-9211 mobile
717-299-3611 office     "Great people, providing quality products that help 
save lives"

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Aaron Peck
Sent: Sunday, September 08, 2013 4:29 AM
To: [email protected]
Subject: Re: flange classes

Thanks for the info.

Well that's all fine and dandy but the old configuration couldn't support more 
than we did. So we have to bolt it directly on the pump. Not the best scenario. 
It "could" have been done but would be out of scope and trying to get it in 
scope is nearly impossible. We went off the AHJs engineering feasibility study, 
where they missed it.

>From the AHJ, not Turkmenistan, said it needs to be "good enough" lol. So it 
>won't meet some things in 20, they know that.

Heres the pump setup. 3 electic pumps in parallel, 2 on city power and 1 on 
generator. All Wilo brand, panels are not designed for automatic operation. So 
if the system goes off they have to run down and turn them on. Also the 
generator is not automatic, so if power goes out they have to run down and turn 
it on. The pump are horizontal going in and vertical out, the correct term for 
this style is alluding me at this moment.

Everything about this project stinks but it only has to be "good enough". 
Probably will have to drill the valve and void the listing. Material needs to 
be procured in the states and shipped. The survey team missed the PN16 flange. 
Just sent Class 150 flanged. We'll approve the voiding of the listing from the 
local AHJ representative and proceed.

Luckily though the victaulic groove flange adapters have slotted bolt holes 
designed for it.

Aaron M. Peck SET
NICET IV (Fire)
+1 (202) 407-9079 Skype
+855 (78) 700-407 Cellphone
Sent from my iPhone

On Sep 8, 2013, at 5:05, "[email protected]" <[email protected]> wrote:

> Ampeck,
>
> The European distributors of Viking, Tyco, Victaulic etcetera can supply you 
> off the shelve with FM approved OS&Y valves, drilled with PN16 bolt circles.
> Drilling it yourselves voids the listing.
>
> Is this a horizontal split case pump?
> If so, can't you install the OS&Y valve on the upstream side of the piece of 
> suction pipe mentioned in NFPA 20 (2013) par. 4.14.6.3.2 ?
> Doing so will allow you to connect that suction pipe with a DIN PN16 flange 
> to the pump and with an ASA flange to the OS&Y valve.
>
> On the discharge side you usually won't have an OS&Y valve directly connected 
> to the pump.
> See NFPA 20 (2013) Figure A.4.30(a) and the diagrams in the Appendix.
>
> Best regards,
>
> Frans Stoop
> TOS architecture & fire protection
> Netherlands <[email protected]>
> Tel. +31-24-324 0112
>
>
> At 16:45 6-9-2013 +0500, you wrote:
>> This is not quite sprinkler related but it's dealing with a fire pump and 
>> metric versus imperial units.
>>
>> I have a pump installed by a Turkish contractor. We're revamping the pump 
>> piping to conform as good as we can to NFPA.
>>
>> Well we tried to bolt our OS&Y valve up to their pump and the bolt circle is 
>> a little smaller then ours. Our valves as all from the USA and that's what 
>> the client wants. So now I'm faced with boring out the holes or something to 
>> make them match up.
>>
>> The flange has a PN16 which is less than a 150 class flange, which would be 
>> roughly PN20. Besides machine drilling the holes, anyone run into this 
>> before? We have groove flange adapters that will accommodate the PN16 
>> flange. Just means we'll have to add in a little piece of pipe and order 
>> more groove flange adapters from the states.
>>
>> Thanks!
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>> -----
>> Geen virus gevonden in dit bericht.
>> Gecontroleerd door AVG - www.avg.com
>> Versie: 2013.0.3392 / Virusdatabase: 3222/6642 - datum van uitgifte: 09/06/13
>
> ------------------disclaimer------------------
> Senders and recipients of e-mail should be aware that there is no such thing 
> as a confidential e-mail. On its way between sender and recipient each e-mail 
> message is stored and transfered by numerous servers, each of which can be 
> located anywhere in the world. Some servers keep your e-mail correspondence 
> on storage for a short time only, other servers may store the communication 
> for many years. In some countries the authorities filter all e-mail 
> correspondence passing by and may decide to read your content. Also, many 
> operators of the e-mail servers can easily read your messages.
> ------------------disclaimer------------------
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Confidentiality Notice:  Information in this message, including any 
attachments, is intended only for the personal and confidential use of the 
recipient(s) above named.  The information contained in this message may be 
privileged and confidential, may constitute a trade secret, may be subject to 
the attorney-client privilege and may otherwise be protected from disclosure.  
If you are not the intended recipient of this message, or an agent responsible 
for delivering it to an intended recipient, you are hereby notified that you 
have received this message in error, and that any review, dissemination, 
disclosure, distribution, or copying of this message is strictly prohibited.  
If you received this message in error, please notify the sender immediately, 
delete this message and destroy any hard copy print-outs.  We have taken 
precautions to minimize the risk of transmitting software viruses, but we 
advise you to carry your own virus checks on any attachment to this message.  
We ca
 nnot accept liability for any loss or damage caused by software viruses.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to