We need to replace 3 painted heads in an existing storage room that currently 
has 14.5 k heads. Going to the closest Equivalent head changes the K factor to 
14.0 and it makes enough of a difference that the calks no longer work……

Even if we replace all of the heads in that area with 14.0's it will not work.  
Does anyone happen to have these laying around?

Question - if we can't find them, what should we do? The calcs do not work due 
to a combination of a slightly degraded water supply and being incorrectly 
calculated by the original installing contractor  - we have the original 
drawings and they used a .15 density throughout the building instead of the 
required .20. (yes- even when originally installed). The difference is only a 
few pounds, but it goes from slightly positive to negative. The AHJ has closed 
his ears and eyes and said "get the painted heads replaced". 

Thanks for your help.
Greg